Is there a ceiling or are these just attached to a duct drop?  How far down are 
they from the sprinklers?

Have you looked at Chapter 8 of NFPA 13 for the obstruction rules?  Over 48" 
isn't the only time you need to be addressing obstructions.



Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Thomas Reinhardt
Sent: Tuesday, June 17, 2014 6:50 PM
To: [email protected]
Subject: Round Ceiling Diffusers

Question for the group. I have a large industrial warehouse fully sprinklered. 
There are numerous round ceiling diffusers that are approximately 5 and half 
foot diameter. Does the 4 foot rule apply. Do they need sprinklers underneath. 
Thanks