To give it some perspective, I'm currently designing the water supply for a two 
storey storage building. The stored water will supply the building sprinklers 
and a dry fire hydrant for the fire department. The water is to be stored in an 
underground tank outside the building and pumped out using a vertical turbine 
fire pump. The capacity of the tank is 100,000 US gallons. The building is 
within city limits, but in the outskirts, so no municipal supply.

Tony

----- Original Message -----
From: "Reza Esmaeili" <[email protected]>
To: [email protected]
Sent: Friday, June 27, 2014 11:03:45 AM
Subject: Re: Water Tank is so Big!

Dear all,
Thanks for all the comments, here I answer some of the questions:
- There is no necessity to follow any cods in Iraq, there is no national code 
for fire.
- The AHJ is Fire Department, they don't have any knowledge about fire 
sprinklers and they let us design as we wish.
- There is no central monitoring.
- I suppose that in case of fire, it takes about 15 minutes for fire 
departments to come.

In the US public water supply is adequate for fire protection in most of the 
big cities and you never have to consider such a big water tank for every 
office building.
While our public water supply is not enough and only available 5 hours a day 
and doesn't have the pressure even to go to the first floor! 

Regards,
Reza
Etalon Security,
Erbil - Iraq
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to