There are so many things wrong here. But, you may be able to make this work 
regardless. Did you take your 75% reduction in fire flow based on the fully 
sprinklered exception in B105.2? If you are starting at 4000 gpm, the required 
flow can be reduced to 1500 gpm if fully sprinklered. Doesn't that work with 
your pumps?  

Duane

----- Original Message -----
From: Johnson, Duane (NIH/OD/ORS) [C]
Sent: Saturday, July 19, 2014 07:51 AM Eastern Standard Time
To: '[email protected]' 
<[email protected]>
Subject: Re: Segue to AHJ's from CPVC Underground

Has Annex B been adopted?  See 101.2.1? 

Duane

----- Original Message -----
From: [email protected] [mailto:[email protected]]
Sent: Saturday, July 19, 2014 07:35 AM Eastern Standard Time
To: [email protected] 
<[email protected]>
Subject: Re: Segue to AHJ's from CPVC Underground

Hi John,
What Ron didn't say is that the AHJ is trying to connect chapter 5 of the IFC 
and table B105.2 fire flow requirements to our sprinkler system pumps. We 
conceded early on to furnish a redundant pump because it was specified that 
way, but the FM is expecting the fire pumps to provide the 4000 GPM from B105.2 
at the sprinkler (ESFR) demand pressure (165 PSI) and do so at the 100% design 
point of the fire pump. We submitted our design with two 1500 GPM pumps piped 
in parallel along with calcs for the storage sprinklers flowing at around 165 
PSI at the pump discharge. The city water system which supplies the project 
flow tested at 5700 GPM at 74 PSI from two 4" hydrant butts. No one at the 
AHJ's office understands how to read a fire code, or any other code for that 
matter. They are "Code Alchemist", taking a paragraph from chapter 5,  table 
from the annex, and numbers from our calcs, mix 'em all together in an AHJ 
beaker and BOOM!! "Minimum code requirement". See? This stuff ain't
  all that hard.

Mark at Aero
602 820-7894

Sent from my iPad

On Jul 19, 2014, at 2:24 AM, "John Drucker" 
<[email protected]<mailto:[email protected]>> wrote:

Like how you wrote; " everything is per code except we have".  "Except" ?, Are 
you/they saying that having two pumps rather than one is a violation; I.e. " 
4000 GPM at 160 vs 4000 at 165" and you're short 5 psi ?  So two code 
violations, two pumps and short 5 psi. Now before you chop my head off, 
consider two things wheres the one pump and 165 psi coming from ? Somehow 
apparently this has been planted in the ahjs head, I'm certain he/she didn't 
come up with it on there own. Now you're stuck.  Frankly and using common sense 
are you hitting demand, does everything fit and work together, is the principal 
designer and owner ok with it ?  Move forward.

John Drucker - Mobile Email
[email protected]<mailto:[email protected]><mailto:[email protected]>
Cell/Text 732-904-6823


[email protected]<mailto:[email protected]> wrote:

How about everything is per code except we have two pumps rather than one.and 
we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most ignorant thing 
I have ever seen. Just found out the chief told plan reviewer no more written 
correspondence. I guess because they don't want a written orecord of their 
stupidity. Please forgive my frustration but I just don't know where to go from 
here..

Ron fletcher Sent from my iPhone

On Jul 18, 2014, at 4:24 PM, "John Drucker - Home" 
<[email protected]<mailto:[email protected]>> wrote:

Ron, et.al.

I don't know the particulars of your situation but we have a saying; there's
your side, their side and the truth.  Perhaps there's an issue with the code
itself,  a local amendment or interpretation. There's got to be something
driving this.

Case in point about a reference standard, NFPA-72 speaks of wall mounted
smoke detectors/alarms and calls out a distance yet the illustration in the
annex is worded differently than the code.

29.8.3.3 Wall Mounting. Smoke alarms or smoke detectors mounted on walls
shall be located NOT FARTHER than 12 in. (300 mm) from the adjoining ceiling
surface.

Yet the annex A.29.8.3 notes;  "Measurements shown are to the closest edge
of the detector".

According to the annex this would place part or most of the alarm or
detector FARTHER than 12 in. from the adjoining ceiling surface.

It's important to note that Annex A opens with the following statement;

"Annex A is not a part of the requirements of this NFPA document but is
included for informational purposes only. This annex contains explanatory
material, numbered to correspond with the applicable text paragraphs"

Yet when brought to NFPA's attention the answer from the NFPA representative
was interpreted from the Annex material.  This is clearly incorrect, the
annex and the illustration are not part of the code.  In either case fix the
code language or the annex.   The same happens in I Code Commentaries and
various subject matter books that often interpret, amend or supplement the
actual code language.  In a nutshell our codes and standards have become a
maze of requirements, exceptions and interpretations.  This should be a
warning flag to the code community.  Perhaps the code official has just
reached his limit and is instead relying on empirical experience in the face
of confusion.

I have situation at this very moment on two different projects that impose
an operational issue for the fire department, one that the code is not
considering.  However my approach is to get everyone around the table do
some brainstorming and come up with an equitable technical solution.
Perhaps by finding the root cause of your situation the stakeholders will
put down their swords and solve the problem.   Food for thought.

Best wishes, always available should the need arise.

Sincerely,

John

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected]<mailto:[email protected]>
Cell/Text: 732-904-6823

Safe Buildings Save Lives !












-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]<mailto:[email protected]>
Sent: Friday, July 18, 2014 1:04 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Segue to AHJ's from CPVC Underground

It's Friday so I figured I'd whine on the forum.  To set the stage, prior to
the letter I am referring to we had approved permitted drawings from the
AHJ. The following is a quote from a letter we received from that same AHJ.

"At this time , Blah Blah Blah Fire Protection District is denying said
plans and is requesting a re-submittal of new plans that exceed IFC, UFC,
and NFPA standards." Nowhere in the body of the letter does he say exactly
how we are to "EXCEED" IFC, UFC and NFPA. In the letter they basically
outline that what was submitted meets the all of the codes. I was told by
the author of the letter at a meeting the day before that he didn't care
what the code said because he is the AHJ and per Section 104 of the IFC he
can make us do whatever he wants. Then he said "do it my way or there will
be no Certificate of Occupancy."  We are 4-5 weeks away from a CofO and the
change involves increasing the size of two new diesel pumps that are being
installed. The fire chief told us to go to the State Fire Marshal if we
wanted to appeal. I'm a bit frustrated with AHJ's right now.

Ron F
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to