I feel your pain.
Ron F 

Ron fletcher Sent from my iPhone

> On Jul 21, 2014, at 12:10 PM, "Tony Liddic" 
> <tony.lid...@mrhsprinklerdesign.com> wrote:
> 
> AHJ has spoken with Mfr Rep directly and has basically decided to forgo
> common sense.
> 
> The only way he will approve it is if NFPA 13R includes this situation
> specifically, ie. "CPVC piping shall be permitted to be installed
> underground below breezeways on system side of riser."
> 
> Thanks,
> 
> Tony Liddic, CET
> MRH Sprinkler Design LLC
> 356 Laurel Glen Dr.
> Springboro, OH  45066
> 937-369-7926
> http://mrhsprinklerdesign.com
> tony.lid...@mrhsprinklerdesign.com
> 
> 
> 
> On Mon, Jul 21, 2014 at 1:22 PM, Fairchild, Jack <
> jfairch...@ballinger-ae.com> wrote:
> 
>> Is it written somewhere that steel is allowed for underground use on the
>> system side?
>> 
>> Jack Fairchild
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tim Stone
>> Sent: Saturday, July 19, 2014 4:43 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: FW: Blazemaster CPVC Underground
>> 
>> FYI
>> 
>> 
>> 
>> Regards,
>> 
>> G. Tim Stone
>> 
>> 
>> 
>> G. Tim Stone Consulting, LLC
>> 
>> NICET Level III Engineering Technician
>> 
>> Fire Protection Sprinkler Design
>> 
>> and Consulting Services
>> 
>> 
>> 
>>                117 Old Stage Rd. - Essex Jct., VT. 05452
>> 
>> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>> 
>>                           tston...@comcast.net <mailto:
>> tston...@comcast.net>
>> 
>> 
>> 
>> From: Lemire, Mark [mailto:mark.lem...@lubrizol.com]
>> Sent: Friday, July 18, 2014 9:02 PM
>> To: Tim Stone
>> Subject: Fwd: Blazemaster CPVC Underground
>> 
>> 
>> 
>> Good evening,
>> 
>> 
>> 
>> Please review John's comments who us one of Lubrizol's Field Tech
>> Specialist.
>> 
>> 
>> 
>> Have a great weekend!
>> 
>> Mark E. Lemire
>> 
>> Piping System Consultant
>> 
>> The Lubrizol Corporation
>> 
>> Representing FlowGuard GoldR, BlazeMasterR and CorzanR CPVC piping systems
>> 
>> 603-738-3101
>> 
>> 603-934-3360 fax
>> 
>> mark.lem...@lubrizol.com <mailto:mark.lem...@lubrizol.com>
>> 
>> www.lubrizolcpvc.com <http://www.lubrizolcpvc.com>
>> 
>> 
>> 
>> 
>> Begin forwarded message:
>> 
>> From: "Pritchard, John" <john.pritch...@lubrizol.com <mailto:
>> john.pritch...@lubrizol.com> >
>> Date: July 18, 2014 at 10:06:15 AM EDT
>> To: "Lemire, Mark" <mark.lem...@lubrizol.com <mailto:
>> mark.lem...@lubrizol.com> >
>> Subject: RE: Blazemaster CPVC Underground
>> 
>> I e-mailed Peter because the original e-mail was from his territory.
>> 
>> 
>> 
>> The AHJ is 100 wrong.
>> 
>> 
>> 
>> CPVC is approved for underground.
>> 
>> 
>> 
>> 13R allows any material approved for Underground water.
>> 
>> 
>> 
>> The way the system is being run which is common in my part of the country
>> the CPVC pipe is part of the sprinkler system and it is approved for
>> underground installations. The AHJ needs to be educated
>> 
>> 
>> 
>> 
>> 
>> John Pritchard
>> 
>> Piping Systems Consultant
>> 
>> The Lubrizol Corporation
>> 
>> Representing FlowGuard GoldR, BlazeMasterR and CorzanR CPVC piping systems
>> 
>> 224-735-3042  office
>> 
>> 312-215-2089  cell
>> 
>> 224-735-3043 fax
>> 
>> <mailto:john.pritch...@lubrizol.com> john.pritch...@lubrizol.com
>> 
>> <http://www.lubrizolcpvc.com/> www.lubrizolcpvc.com
>> 
>> 
>> 
>> From: Lemire, Mark
>> Sent: Friday, July 18, 2014 9:03 AM
>> To: Pritchard, John
>> Subject: Fwd: Blazemaster CPVC Underground
>> 
>> 
>> 
>> Any comments!
>> 
>> Mark Lemire
>> 
>> Piping Systems Consultant
>> 
>> The Lubrizol Corporation
>> 
>> Representing FlowGuard Gold, BlazeMaster and Corzan CPVC piping systems
>> 
>> 603-738-3101 cell
>> 
>> 603-934-3360 fax
>> 
>> Email: mark.lem...@lubrizol.com <mailto:mark.lem...@lubrizol.com>
>> 
>> Website: www.lubrizolcpvc.com <http://www.lubrizolcpvc.com>
>> 
>> 
>> Begin forwarded message:
>> 
>> From: Tim Stone <tston...@comcast.net <mailto:tston...@comcast.net> >
>> Date: July 18, 2014 at 10:00:55 AM EDT
>> To: <mark.lem...@lubrizol.com <mailto:mark.lem...@lubrizol.com> >
>> Subject: FW: Blazemaster CPVC Underground
>> 
>> Mark,
>> 
>> The attached email is from The AFSA Forum.
>> 
>> Can you way in?
>> 
>> Regards,
>> G. Tim Stone
>> 
>> G. Tim Stone Consulting, LLC
>> NICET Level III Engineering Technician
>> Fire Protection Sprinkler Design
>> and Consulting Services
>> 
>>                117 Old Stage Rd. - Essex Jct., VT. 05452
>> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>>                           tston...@comcast.net <mailto:
>> tston...@comcast.net>
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> sprinklerforum-boun...@lists.firesprinkler.org]
>> On Behalf Of rfletc...@aerofire.com <mailto:rfletc...@aerofire.com>
>> Sent: Friday, July 18, 2014 9:46 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> <mailto:sprinklerforum@lists.firesprinkler.org>
>> Subject: RE: Blazemaster CPVC Underground
>> 
>> That's a good one. I'll add that to my "so you think you have heard
>> everything" list. Like saying it's approved below a valve but not above.
>> Does he have a code reference or is this it just their opinion? Can you
>> have someone from the manufacturer call them?
>> Ron F
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> sprinklerforum-boun...@lists.firesprinkler.org]
>> On Behalf Of Tony Liddic
>> Sent: Friday, July 18, 2014 6:18 AM
>> To: sprinklerforum
>> Subject: Blazemaster CPVC Underground
>> 
>> I have a client that does a lot of typical apartment building in various
>> jurisdictions. The buildings are 3 stories with breezeways 1/3 of the way
>> down the length of the building.
>> 
>> They are 13R systems and the client has always used Blazemaster CPVC. They
>> run a main down the center of the 1st floor, drop below the breezeway
>> underground then back up in a wall on the other side. This has never been
>> an issue until now.
>> 
>> An AHJ is stating that the CPVC is not approved for underground use on the
>> system side of the riser, only the supply side.
>> 
>> Any thoughts?
>> 
>> Thanks,
>> 
>> Tony Liddic, CET
>> MRH Sprinkler Design LLC
>> 356 Laurel Glen Dr.
>> Springboro, OH  45066
>> 937-369-7926
>> http://mrhsprinklerdesign.com
>> tony.lid...@mrhsprinklerdesign.com
>> <mailto:tony.lid...@mrhsprinklerdesign.com>
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> <mailto:Sprinklerforum@lists.firesprinkler.org>
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> <mailto:Sprinklerforum@lists.firesprinkler.org>
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> 
>> 
>>  _____
>> 
>> 
>> 
>> Both the individual sending this e-mail and The Lubrizol Corporation
>> intend that this electronic message be used exclusively by the individual
>> or entity to which it is intended to be addressed. This message may contain
>> information that is privileged, confidential and thereby exempt and
>> protected from unauthorized disclosure under applicable law. If the reader
>> of this message is not the intended recipient, or an employee or agent
>> responsible for delivering the message to the intended recipient, be aware
>> that any disclosure, dissemination, distribution or copying of this
>> communication, or the use of its contents, is not authorized and is
>> strictly prohibited. If you have received this communication and are not
>> the intended recipient, please notify the sender immediately and
>> permanently delete the original message from your e-mail system.
>> 
>> http://online.lubrizol.com/email/disclaimer/cliquez_ici_pour_traduction_en_f
>> rancais.htm
>> 
>> http://online.lubrizol.com/email/disclaimer/Klicken_Sie_hier_fur_die_deutsch
>> e_Ubersetzung.htm
>> 
>> http://online.lubrizol.com/email/disclaimer/Clicar_aqui_para_versao_em_Portu
>> gues.htm
>> 
>> http://online.lubrizol.com/email/disclaimer/De_un_clic_aqui_para_su_traducci
>> on_al_espanol.htm
>> http://online.lubrizol.com/email/disclaimer/Chinese.htm
>> http://online.lubrizol.com/email/disclaimer/Japanese.htm
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org