Brian:

As I'm sure you know, the standard was titled for many years,
"Installation of Sprinkler Systems in Residential Occupancies up to and
Including Four Stories in Height", but is now titled, "... in Low-Rise
Residential Occupancies".   (For whatever it's worth, I voted against
this as it's vague and not entirely aligned with existing definitions in
code(s) and standard(s).    However, in the 2013, Section 1.1 it very
clearly states that the standard covers residential occupancies up to
60' (18 m) above grade plane (as defined in the applicable building
code).  The annex material clarifies that this height is coincidental to
the limit for Type V construction, and so is aligned with the code in
that regard and implies intent to most closely manage Type V buildings,
which are almost always wood framed in R-group occupancies.   So
literally and as written, if you have a 5- or 6-story building where the
height of the highest floor is 60' or less and it's of a construction
type other than Type V-A (which the code limits to 4 STORIES), then the
answer to your question (surprisingly) is yes, you can use 13R, taking
it literally as it's written.

But keep in mind that this is all about what your locally adopted code
allows, and the code generally tells us when we can and can't use a
particular type of sprinkler system.   You can't take a 13R for an extra
story except in R-2, and you can't take it in lieu of fire resistive
construction.  And just because 13R leaves itself open to application in
buildings of Type III or II construction that may exceed four stories,
your code or building official may not.  Also remember that if your code
doesn't reference the 2013 NFPA sprinkler standards, the older editions
are still implicitly limited to four stories.

The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 13D/13R Technical Committee on Residential
Sprinkler Systems.  Not only that, this is a slippery slope so I also
disclaim the email chatter that's sure to follow, the second guessing
and the uproar.

Steve Leyton
Protection Design & Consulting
San Diego, CA



-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Brian Harris
Sent: Monday, July 28, 2014 8:40 AM
To: [email protected]
Subject: 6 Story Hotel

Having a little debate here in the office..... Looking at a 6 story
hotel and (1) person wants to use NFPA-13R & (1) says you can't because
it's over 4 stories and you must use NFPA-13. Comments welcome .... :)

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to