We have had several projects rejected by the plans examiner recently because
we didn't hydraulically calculate each floor.  These are multi-story
residential projects with typical floor plans.  Some of the projects are
zoned per floor, but others are piped with the main on the first floor and
supplied with the CPVC branch lines running vertically through the walls.
This is possible, as mentioned, due to the identical nature of the unit
layout of each floor.

 

The Section Manager of the sprinkler review department evidently interprets
the standard to require hydraulic calculations for every floor, regardless
of typicality.  Does anyone see this as a correct interpretation or
necessary?  I've asked him to provide the section of the standard that he is
relying on to justify this.  

 

It seems somewhat burdensome, considering all things remaining the same
except a drop in elevation, one could reasonably expect an increase in
available pressure to the system on the floor below.

 

Curtis Tower

Sr. Fire Protection Specialist

Central Fire Protection

Office:  (214) 496-9797

Mobile:  (682) 667-0323

Fax:  (214) 496-9201

 