This is an issue that has been lurking in the shadows for a while.  The 24ā€ is 
the maximum width of a flue.  The 3.5 ft dimension is still in play but only 
for defining the type of rack. SO if you have too narrow an aisle, the fire 
will jump the aisle so the criteria for the individual rack type is expected to 
be inadequate for the larger overall assembly.  For example, you have 2 single 
row racks (SRR) that are separated by a 30 inch aisle.  The overall assembly is 
classified as a double row rack (DRR).  So in attempting to apply the DDR 
criteria, where do you place the longitudinal in-rack sprinklers?  The TC said 
this cycle that in-rack sprinklers shall be located only in flues so you can 
not place them in narrow aisles.  Now lets say you have 5 DRR with 30ā€ aisles.  
The overall assembly is a multiple row rack (MRR).  The MRR criteria is 
typically equally spaced in-racks down the transverse flue (often at 10 ft).  
We know you must have an in-rack at the intersection of the longitudinal and 
transverse flues to have effective protection of a DRR.  So WHERE do we place 
the in-rack sprinklers among these close DRR's that are called a MRR.  Beats 
the dog foo out of me as did trying to get this addressed during this cycle.  
Pushing a 500 lb rock uphill can be easier than getting the majority of 30 
people to see the problem much less fixing it.  Yea I’m still a little 
frustrated.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Aug 6, 2014, at 4:27 AM, Martinez, Dewayne <[email protected]> 
wrote:

> After checking the definition 3.9.3.7.1is 3.5ft the magic number?
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> Martinez, Dewayne
> Sent: Wednesday, August 06, 2014 6:10 AM
> To: [email protected]
> Subject: rack flue space width
> 
> NFPA 13 (07ed)
> 
> Double row racks
> 
> Is there a limit to how wide a flue space can be between double row
> racks before you have to figure protection in each rack individually?
> 
> 
> 
> I am figuring a job where 2 sets of double row racks have a 2' wide flue
> space between them due to columns.
> 
> 
> 
> Thanks,
> 
> Dewayne
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to