Ladies/Gentlemen:
 
The last time I checked, all new sprinklers manufactured at U.S. plants are 
"shock-tested" to a minimum of 500 psi -  one heckuva water 'hammer'. In my 
humble opinion, I do believe  something else (overhead pipe/fittings, 
underground, FDC, etc.) would give out  before a pressure 'surge' would cause a 
sprinkler head to activate. In 40 years  - and many "accidental" activation 
cases later - I've never seen it  happen...Heard secondhand, but never 
actually been able to verify it  happened. Just my 1.5 cents, adjusted for 
deflation.
 
Regards to All-
 
Jerry*
[email protected]_ (mailto:[email protected]) 
 
Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.
Santa Fe, New Mexico USA
(800) 503.1961 nationwide
 
*NM Sprinkler Journeyman Lic. #08228
 
 
 
In a message dated 8/6/2014 2:26:58 P.M. Mountain Daylight Time,  
[email protected] writes:

If it  were due to a pressure spike than only one head opening might not  be
unusual as the over pressure would be immediately relieved, but an  unlikely
event nevertheless. Particularly multiple times unless a batch of  bad
sprinklers. Think of pieces of pipe cut from a single pipe with a bad  seam.
Then again when the forklift guy hits the sprinkler it usually is  an
accident.


On Wed, Aug 6, 2014 at 9:28 AM, Steve Leyton  <[email protected]>
wrote:

> Actually sprinklers  (and most UL-listed equipment) are required to be
> pressure tested at  4x rated, so that would be 700 PSI for conventional
> sprinklers and  1000 PSI for HP.
>
>  SL
>
>
>
>
>
>
> -----Original  Message-----
> From: Sprinklerforum [mailto:
>  [email protected]] On Behalf Of
>  [email protected]
> Sent: Wednesday, August 06, 2014 9:08 AM
>  To: [email protected]
> Subject: RE: Excessive  system pressure and opening of sprinklers
>
> Check the UL listing  requirements, I believe the sprinkler heads are
> pressure tested at 500  PSI.
> Mark at Aero
>
> -----Original Message-----
>  From: Sprinklerforum [mailto:
>  [email protected]] On Behalf Of
>  [email protected]
> Sent: Wednesday, August 06, 2014 9:05 AM
>  To: [email protected]
> Subject: Excessive system  pressure and opening of sprinklers
>
> Got a client that has had  more than one incident of "accidental" 
sprinkler
> discharge they claim  is due to municipal pressure surges.   Static 
pressure
> on  this industrial system is 150 psi, and a surge tank was installed a
>  couple of years back to mitigate alleged pressure spikes.
>
>  Anyone heard of sprinklers opening due to a pressure spike?
>
> It  was only one head out of multiple hundreds in the building.
>
>  Craig L. Prahl
> Fire Protection Group Lead
> CH2MHILL
>  Lockwood Greene
> 1500 International Drive
> Spartanburg, SC   29303
> Direct - 864.599.4102
> Fax - 864.599.8439
>  CH2MHILL Extension  74102
> [email protected]
>
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerfo
rum-firesprinkler.org
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



--  
Ron Greenman
Instructor
Fire Protection Engineering  Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA  98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700  (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS,  WSAFM, WFC, WFSC

They are happy men whose natures sort with their  vocations. -Francis Bacon,
essayist, philosopher, and statesman  (1561-1626)

A problem well stated is a problem half solved. -Charles F.  Kettering,
inventor and engineer  (1876-1958)
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to