That my read on it also, I was told to pose the question, I'm just an old guy 
with 36 years' experience, 122 day from retirement. What do I know?


Richard L. Mote ET
Design Manager
Rowe Sprinkler Systems, Inc.



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hill
Sent: Wednesday, August 13, 2014 11:54 AM
To: [email protected]
Subject: RE: ESFR & Sprinkler in Racks.

16.3.3.2 does not say you can use ESFR with solid shelves as long as in rack 
protection is required. I would say that if there are solid shelves, ESFR 
sprinklers are out.

Mike Hill

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Richard Mote
Sent: Wednesday, August 13, 2014 11:39 AM
To: [email protected]
Subject: ESFR & Sprinkler in Racks.

Here is the scenario;

New  warehouse addition to an existing sprinklered automotive parts 
distribution warehouse.
Peak height = 36'-1", Rack height = 28'.
Addition was originally specified for an ESFR system with racks. They came back 
and said they wanted to be able to store small quantities of flammable liquids. 
The insurance reviewer said OK add 1 level of in rack sprinkler where the 
flammable liquid  storage would be. The customer said, we don't know it may 
move around depending on how much we have at any given time, so install 
sprinkler in all the racks. Yesterday I get the final rack layout drawings 
which call for solid steel shelving at the 12' and 28' levels. I responded that 
per NFPA 13, 2007 (the current recognized addition in PA)
16.3.3.2 you can't use ESFR with solid shelving.  Now the customer wants to 
know. If we install in-racks at the 27' and 11' levels could we still use ESFR 
at the roof? (sort of defeats the purpose but it's not my money)I have spent 
the last hour going through chapters 16 & 17. I can't find anything that say 
you could do that. But I also haven't found anything that says you can't other 
than 16
 .3.3.2 & 17.2.3.1.1. At this point I want to hang my hat on that and say no we 
can't. However I may be missing something so I thought I would throw it out for 
discussion.

Richard Mote ET
Design Manager
Rowe Sprinkler Systems, Inc.
PO Box 407
Middleburg, PA 17842
P- 877-324-ROWE
F- 570-937-6335
[email protected]<mailto:[email protected]>
www.rowesprinkler.com<http://www.rowesprinkler.com/>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to