>From NFPA 1 (2012) with cross references to NFPA 101. Note that the last 
>sentence in the Annex implies that the equipment in concealed spaces should 
>also be removed.

4.5.8.3* Existing life safety features obvious to the public, if
not required by the Code, shall be either maintained or removed.
[101:4.6.12.3]

A.4.5.8.3 Examples of such features include automatic sprinklers,
fire alarm systems, standpipes, and portable fire extinguishers.
The presence of a life safety feature, such as sprinklers
or fire alarm devices, creates a reasonable expectation by
the public that these safety features are functional. When systems
are inoperable or taken out of service but the devices
remain, they present a false sense of safety. Also, before taking
any life safety features out of service, extreme care needs to be
exercised to ensure that the feature is not required, was not
originally provided as an alternative or equivalent, or is no
longer required due to other new requirements in the current
Code. It is not intended that the entire system or protection
feature be removed. Instead, components such as sprinklers,
initiating devices, notification appliances, standpipe hose, and
exit systems should be removed to reduce the likelihood of
relying on inoperable systems or features. Conversely, equipment,
such as fire or smoke dampers, that is not obvious to the
public should be able to be taken out of service if no longer
required by this Code. [101: A.4.6.12.3]

Yes, it is true that we install sprinklers in concealed spaces that are not 
"visually" inspected because it is not required by NFPA 25. However, those 
situations are required by code. This situation provides an inherent risk with 
no real benefit. Can you imagine the egg on your face/the industry if someone 
tried to punch a wire/conduit through the wall and activated the sprinkler 
causing water damage? I say take it out.

Duane Johnson, PE
Design Manager
Strickland Fire Protection
5113 Berwyn Road
College Park, Md. 20740
301-474-1136 Office
301-455-0010 Cell
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Martinez, Dewayne
Sent: Tuesday, August 19, 2014 6:47 AM
To: [email protected]
Subject: sprinklers buried in walls

I have a job that has an existing upright sprinkler system in which the GC has 
already built the walls to the deck and has encased some of the existing 
sprinkler heads in the walls.  He is asking if we can just leave them and cut 
in new heads as needed.  Is this acceptable per NFPA 13?

Thanks,

Dewayne 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to