Good morning to All:
 
My past experience says that (where the sprinklers are in the  walls) - 
someone is going to come along and drive a screw, nail, punch a hole  for 
whatever reason and then, Bingo. My fear is future wall penetrations - we  have 
experienced this with the sprinkler piping when we ran vertically  up walls 
with sidewalls, sure enough, some drove screws in to the CPVC "hidden"  in 
the walls. Code or no Code, they are asking for real trouble. Won't  even 
hazard a guess as to how the insurance carrier would handle the  "loss"...
 
Regards-
 
Jerry
[email protected]_ (mailto:[email protected]) 
 
Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.*
Santa Fe, New Mexico USA
(800) 503.1961 nationwide
 
*Licensed Fire Protection Engineers -  Architects/Inspectors/Fire 
Investigators:  AZ  CA  CO   NM  NV  NY  TX  UT  KS  MD  MS
 
**PE/FPE/Consultants to Fire Sprinkler Contractors  Nationwide
 
 
 
 
In a message dated 8/19/2014 5:43:53 A.M. Mountain Daylight Time,  
[email protected] writes:

>From  NFPA 1 (2012) with cross references to NFPA 101. Note that the last 
sentence  in the Annex implies that the equipment in concealed spaces should 
also be  removed.

4.5.8.3* Existing life safety features obvious to the public,  if
not required by the Code, shall be either maintained or  removed.
[101:4.6.12.3]

A.4.5.8.3 Examples of such features include  automatic sprinklers,
fire alarm systems, standpipes, and portable fire  extinguishers.
The presence of a life safety feature, such as  sprinklers
or fire alarm devices, creates a reasonable expectation  by
the public that these safety features are functional. When  systems
are inoperable or taken out of service but the devices
remain,  they present a false sense of safety. Also, before taking
any life safety  features out of service, extreme care needs to be
exercised to ensure that  the feature is not required, was not
originally provided as an alternative  or equivalent, or is no
longer required due to other new requirements in  the current
Code. It is not intended that the entire system or  protection
feature be removed. Instead, components such as  sprinklers,
initiating devices, notification appliances, standpipe hose,  and
exit systems should be removed to reduce the likelihood of
relying  on inoperable systems or features. Conversely, equipment,
such as fire or  smoke dampers, that is not obvious to the
public should be able to be taken  out of service if no longer
required by this Code. [101:  A.4.6.12.3]

Yes, it is true that we install sprinklers in concealed  spaces that are 
not "visually" inspected because it is not required by NFPA  25. However, 
those situations are required by code. This situation provides an  inherent 
risk 
with no real benefit. Can you imagine the egg on your face/the  industry if 
someone tried to punch a wire/conduit through the wall and  activated the 
sprinkler causing water damage? I say take it out.

Duane  Johnson, PE
Design Manager
Strickland Fire Protection
5113 Berwyn  Road
College Park, Md. 20740
301-474-1136 Office
301-455-0010  Cell
[email protected]


-----Original  Message-----
From: Sprinklerforum  
[mailto:[email protected]] On Behalf Of Martinez,  
Dewayne
Sent: Tuesday, August 19, 2014 6:47 AM
To:  [email protected]
Subject: sprinklers buried in  walls

I have a job that has an existing upright sprinkler system in  which the GC 
has already built the walls to the deck and has encased some of  the 
existing sprinkler heads in the walls.  He is asking if we can just  leave them 
and cut in new heads as needed.  Is this acceptable per NFPA  13?

Thanks,

Dewayne  



_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to