There are provisions for omission of sprinklers in specific areas.  Electrical 
rooms are one example I run into quite often.  BUT, in order to omit the 
sprinklers, other construction and operational measures must be followed as 
listed in both NFPA 13 and the Building/Fire Codes.   If those other 
requirements are met, even though that room may be unsprinklered, the intent of 
"throughout" is still met.

There have been other cases where a substation of fire protection and 
prevention/control measures are required in lieu of sprinklers for a portion of 
a building.  The omission of sprinklers in the one portion did not render the 
building non-compliant with NFPA 8.1.1.

If you have a unique condition it is best to seek opinion and acceptance of the 
AHJ and/or Owners' Underwriter/Risk Consultant.



8.1.1* The requirements for spacing, location, and position of sprinklers shall 
be based on the following principles:
(1) Sprinklers shall be installed throughout the premises.

A.8.1.1 This standard contemplates full sprinkler protection for all areas 
including walk-in
coolers, freezers, bank vaults, and similar areas. Other NFPA standards that 
mandate sprinkler
installation might not require sprinklers in certain areas. Based upon 
experience and testing,
sprinklers have been found to be effective and necessary at heights in excess 
of 50 ft
(15.2 m). For a building to meet the intended level of protection afforded by 
NFPA 13, sprinklers
must not be omitted from such high ceiling spaces. The requirements of this 
standard
should be used insofar as they are applicable. The authority having 
jurisdiction should be consulted
in each case. A building is considered sprinklered throughout when protected in 
accordance
with the requirements of this standard.


Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jamie Seidl
Sent: Wednesday, August 20, 2014 8:34 AM
To: [email protected]
Subject: fully sprinklered definition

I seem to remember that there was a paragraph in NFPA 13 that a building is 
considered fully sprinklered even when areas remain sprinklered where allowable 
by this standard.  Did I just dream this?  I can not find it this morning.
Thanks,
Jamie
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to