Although not well emphasized and inconsistently stated Vertical placement is APPROXIMATE and horizontal is a maximum. Look at the sub-titles of Table 16.3.1.1
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Aug 20, 2014, at 11:26 AM, Bob <[email protected]> wrote: > Let me rephrase my question, where would the intersection of the transverse > flue and longitudinal flue be? Is it literally between loads as the figures > in 13 show, or can the intersection be anywhere along the height of the load > up to the maximum of 10'? > > Thank You, > > Bob Knight, CET III _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org