Tim,
I don't know all that much about fire retardants and expanded
plastics. However if you're looking at Rack storage to 25' high, you'll
need to look at chapter 17, rather than 15.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 8/29/2014 10:17 AM, Tim Stone wrote:
Existing Warehouse, 35' high roof, 25'H Storage mixed Group A plastics in
racks including high piled pallet storage of expanded polystyrene Styrofoam
blocks.
NFPA 13, Table 15.4.1, Exposed expanded plastics, allows the use of ESFR, K
25.2, Pendent at 60 PSI in a building with Max Ceiling height of 40'.
Question: What level of fire retardant would be required on this product to
reduce Sprinkler System requirements? I have MSDS and manufactures
literature (which discuss fire retardant in product) if needed.
Would any fire retardant built into the product help?
Thank you in advance.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343
<mailto:[email protected]>
[email protected]