Sorry, C=80 I believe 

> On Aug 29, 2014, at 4:46 PM, Brad Casterline <[email protected]> wrote:
> 
> At one time 13 said for 50 year old underground C=100. I do not see it in the 
> '07, just that the AHJ is permitted to consider other C values.
> 
>> On Aug 29, 2014, at 4:31 PM, Travis Mack <[email protected]> wrote:
>> 
>> This was not brought up in project specs or plans.  Nor was it brought up in 
>> plan review.  This was a project that had an existing 4" ductile supply 
>> line.  It is supplying some paint booths and some exhaust ducts in an 
>> otherwise unsprinklered building.  When the guys did the forward flow test 
>> of the new backflow preventer, there was an issue that they weren't getting 
>> as much water as they thought it should have.  So, the EOR for the project 
>> comes back and says something about the calcs.  According to my customer, 
>> the EOR says per a "chart" the C-Factor should have been 60 instead of 140.  
>> For 3 of the 4 paint booths, it is not a problem.  They are small and plenty 
>> of margin.  For the 4th, we end up with a problem.  But, if there is nothing 
>> in the specs or criteria to cause the modification of that pipe, I am not 
>> sure where it will go.  The good thing is that we still have a margin on the 
>> system, but it is less than the 10% required.
>> 
>> I have just never heard of having to do this modification.  I wanted to make 
>> sure it was something I have not been missing.
>> 
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>> 
>>> On 8/29/2014 2:20 PM, Mark A. Sornsin, P.E. wrote:
>>> Travis,
>>> 
>>> Off-hand I can offer no help.
>>> 
>>> But I am curious to see the responses. Had the engineer denoted the 
>>> requirement in the project drawings or specs, I'd definitely side with 
>>> them.  If not, then I want to know if he has a leg to stand on (i.e. code 
>>> reference).
>>> 
>>> This CAN be a significant issue and is another example of a potentially 
>>> serious 'miss' by engineers who don't do their jobs with regards to 
>>> sprinkler system drawings/specs. E.g., take a 200 ft. run of existing 6 in. 
>>> pipe - 50 years old.  They tell you to use it to modify the existing pipe 
>>> schedule sprinkler system to meet the new occupancy. Most often, a 
>>> contractor can get away with simply assuming it is 6" ductile with a 
>>> c-factor of 140. But what if in reality it is unlined cast iron?  What 
>>> C-factor are you to use?
>>> 
>>> FM taught me that it depended on the water corrosiveness.  Who determines 
>>> that? I don't know if the FM data is acquired from anything that could be 
>>> cited by code. Their tables say 50 yr old cast iron in mildly corrosive 
>>> ware should have a C-factor of 75; if corrosiveness is severe, it should be 
>>> 40. At an extra Hazard, Group I demand of 750 gpm, the friction though 100 
>>> feet of pipe can vary from 1.5 psi at C=140; to 4.6 psi at C=75; to 14.9 
>>> psi at C=40.  Pretty significant variance and not something that should be 
>>> blown off by the engineer or designer.
>>> 
>>> Ideally you'd do a water test THOUGH that pipe to verify actual friction 
>>> losses - but that is almost never a viable option. Then again, if you were 
>>> able to do so, you may be able to get a change order when you prove that 
>>> the engineer overlooked a serious issue.
>>> 
>>> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
>>> Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
>>> http://www.kfiengineers.com
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum 
>>> [mailto:[email protected]] On Behalf Of Travis 
>>> Mack
>>> Sent: Friday, August 29, 2014 3:52 PM
>>> To: [email protected]
>>> Subject: Modifications to C-Factor due to age of pipe
>>> 
>>> Does anyone know if there is any requirement in NFPA or Uniform Facilities 
>>> Criteria to modify the C-Factor of existing underground piping based on the 
>>> age of the pipe?  If so, do you have a section reference so I can look it 
>>> up.  An engineer is requiring us to do it, but won't provide the reference. 
>>>  Yeah..It is one of those days.
>>> 
>>> --
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> 2508 E Lodgepole Drive
>>> Gilbert, AZ 85298
>>> 480-505-9271
>>> fax: 866-430-6107
>>> email:[email protected]
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> ______________________________________________________________________
>>> This email has been scanned by the Symantec Email Security.cloud service.
>>> For more information please visit http://www.symanteccloud.com
>>> ______________________________________________________________________
>>> 
>>> ______________________________________________________________________
>>> This email has been scanned by the Symantec Email Security.cloud service.
>>> For more information please visit http://www.symanteccloud.com
>>> ______________________________________________________________________
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to