Is there any experience with review comments or specifications calling for
a flexible coupling on a welded steel discharge pipe supplying water to a
fire pump?

2010 IBC;  2010 NFPA:  U.S. Government job:  Category 4 Occupancy
(essential)
Two independent water supplies (municipal underground and above ground tank)
Frequency of seismic events in this area:  very low, and not strong 10% and
30% of gravity for the 1 and 0.2 second period spectral response
acceleration.

NFPA 22 is the hammer used to justify asking for the flexible coupling.
The only mention of flexible coupling in NFPA 22 is at Figure Annex B.1.x,
for underground fiberglass tanks.

I have not seen a flex coupling for a water tank to separate steel
piping-that-is-fixed-to-the-ground and
steel-pipe-that-is-fixed-to-the-tank,  whether the tank be for water,
liquid petroleum or LNG tanks.  Maybe the Japanese do it, but I have not
seen it in California quake country, either.


*Questions:*
1.  Is there a nationally accepted practice whereby flex-joints are
required between tanks and their ground based piping?
2.  Are flexible connections listed for outdoor service where freezing and
​strong
solar radiation are present?
3.  Would not seismic bracing be sufficient (a method most of the O&G
industry engages) rather than a flex joint ?  Bracing against seismic event
is the approach taken by O&G, and seems to be the intent of NFPA 22
(Sections 13.5.2.2.  and for anchor bolts 5.3.2)
2.  Since we are outside, not indoors, do the requirements of NFPA 13
​bracing apply (there is no direct reference from NPFA 22 to NFPA 13 with
regards to earthquake bracing)
apply, since there is no "structure" with which to make a comparison of
equivalence [3],[4]?

[1].  IBC-2006-Figure1613_5(01) one second period spectral response
[2].  2013/2010 NFPA 24 12.2.5 To minimize or prevent pipe breakage where
subject to earthquakes, aboveground pipe shall be protected in accordance
with the seismic requirements of NFPA 13.
[3].  2010/2013 NFPA 13  Section 9.3.1.2 Alternative methods of providing
earthquake protection of sprinkler systems based on a seismic analysis
certified by a registered professional engineer such that system
performance will be at least equal to that of the *building structure*
under expected seismic  forces shall be permitted.
[4].  2013/2010 NFPA 13 Section 9.3.3.1 An approved seismic separation
assembly shall be installed where sprinkler piping, regardless of
size,  *crosses
building seismic separation joints *at ground level and above.

Additional references
2013 NFPA 22 4.12.4.1 Tank structures shall comply with the local building
code for seismic requirements.
4.12.4.2 Specific design criteria shall be contained in the appropriate
chapter for the particular tank, or in local codes, whichever is more
stringent.
5.3.1 Tanks shall meet the requirements for resistance to earthquake damage
in accordance with the earthquake design provisions of AWWA D100.
​

Personally, I think corrosion, and not earthquake would have been a better
​focus of
taxpayer money
.
​Maybe the specification writers thought to include an
internal tank liner AND a passive cathodic protection system, to extend the
tank life to at least a hundredth of the 1000-year earthquake we are
designing for
.

​Scot Deal
Excelsior Fire/Risk Engineering