I have a large renovation project we've been wrapping up. Due to over head
duct obstructions, we had some sprinklers located about 30" away from
columns. the next sprinkler was on the other side of the column, 14'-0"
away from the first. The fire inspector noted that we would need to add
sprinklers on the other side of the column since we couldn't meet the 3
times rule, and if we did, it would still be too far from the other
sprinkler that was 11'-6" away from the side of the column. I mentioned it
to him and his boss that the 8.6.5.2.1.3 rule was up to a maximum of 24"
away from the column, at that point the column was no longer an
obstruction, and NFPA considered this adequate coverage. He initially
agreed with me yesterday, but we were shot down for a C.O. today because we
didn't add the sprinklers on the opposite side of the column. Normally, I
would have argued the point, but the GC just want's his CO, so he's paying
for the heads. Needless to say, I now look like I don't know what i'm
talking about in the eyes of the owners rep and contractor.
Have I had 8.6.5.2.1.3 wrong all these years? I always thought that 24"
away meant no problem, move on to the next.
Jamie Seidl
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org