Very effective, we use them all the time. 
Ron F

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Hairfield
Sent: Thursday, October 02, 2014 10:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pressure Limiting Drivers

I've used them on numerous projects.
Saves lots of water during the 30 minute weekly run.
Mike

> Date: Thu, 2 Oct 2014 11:44:48 -0600
> From: silva...@shaw.ca
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Pressure Limiting Drivers
> 
> I have a diesel engine driven fire pump that will have a pressure of about 
> 200 psi at churn, including the city supply. My first thought was using a 
> pressure reducing valve downstream of the fire pump. But the pump supplier 
> suggested using a pressure limiting driver on the fire pump. anyone used one 
> before? Any NFPA restrictions?
> 
> Thanks,
> 
> Tony 