What is the minimum distance between UL 142 compliant double wall diesel fuel 
tanks located outside?  All I can find is NFPA 30's 2012 Table 22.4.2.1 
requirement of 1/6 x sum of adjacent tank diameters but not less than 3 ft.  My 
tanks are 5'-5" diameter.  The problem is we have to elevate three of these on 
an elevated platform in a very tight space and our current spacing between is 
2'-6".  In the opinion of the forum, does the minimum spacing of tanks per NFPA 
30 eliminate consideration of any spacing less than 3 ft?

Thank you,

Ryan L. Hinson, PE*, SET
Senior Fire Protection Engineer, Fire Protection Engineering Group
Burns & McDonnell
Direct: 952-656-3662
Mobile: 320-250-5404
Fax: 952-229-2923
www.burnsmcd.com<BLOCKED::www.burnsmcd.com>
*Registered in MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org