Jerry,
Looking at the 2010 ed. 6.6.6 (yikes), crawl spaces are specifically omitted
from requiring sprinklers.  Also, a "test" is provided to determine if
sprinklers are required or not, "other concealed spaces that are not used or
intended for living purposes or storage and do not contain fuel-fired
equipment".
Your situation meets the crawl space omission so there should be no reason
to sprinkle it.  I'm working instead of hunting, my weekend is shot!  Hope
you have a good weekend.