I am looking at a warehouse that has 100 to 300 gallon plastic totes that
are supported by a rack around each tote.  This allows the totes to be
stacked 3 high, for a height of approximately 16'.  These totes are empty
and in the process of being cleaned of any solution that may have been in
them so they can be used by other customers.  As I look in NFPA 13 (2007)
at the definition of stable and unstable piles, it appears that these would
be stable piles, requiring more water than unstable piles.  If there is a
fire in a lower tote, I am sure the fire might extend to a tote above, but
due to the steel racks, they would not fall over.  However, due to the
openness of the racks, the water would be able to get to the bottom of the
pile quickly, hence limiting it to the pile that is on fire.
Would you classify these as stable piles?  The difference is a .4/2500 for
unstable versus .7/2500 for stable.

-- 
*Jay Stough*
NICET IV LAYOUT
NICET III ITM