Some questions I would be asking:

1. Is the paint being removed a solvent based or water based paint?
2. What is the blasting media, is it really sand or another material?
3. Is the removed material captured and removed from the space during the 
process or allowed to accumulate in the room?
4. Are there any other surface prep processes going on in the space that would 
use solvents or other combustible/flammable cleaners?
5. Are there dust collection systems which are part of this process and if yes, 
are they internally protected with an automatic suppression system?
6. What static electricity mitigating protections are in place during the 
blasting process?
7. Is there any grinding, cutting or welding going on near to this process?

The paint flakes are a solid, typically require high energy to ignite if they 
are combustible at all.  A lot of times the dried paint doesn't pose as great a 
hazard as it does when still in liquid form as the solvents evaporate during 
the drying/curing process.  

The greater hazard in these environments is explosion more so than fire.  So 
you won't find a lot of discussion about fire suppression in these particular 
areas.   

There needs to be a bit of an evaluation of the operation to evaluate the 
potential for fire and the severity.  Some operations where careful and proper 
control methods are utilized have a very low fire potential but I've see others 
that make you wonder how they haven't made the six o'clock news.  

As with everything we do, there is no one-size-fits-all answer.


Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Easter, Timothy
Sent: Sunday, November 02, 2014 10:21 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: sand blasting room NFPA 13 hazard classification

I am designing a sand blasting room as ordinary hazard group 2. Is this 
acceptable? Should it be a higher hazard? Is there another NFPA code pertaining 
to a sand blasting room?

Feel free to contact me with any questions.
Regards,

Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
11832 Rock Landing Drive Suite 306
Newport News, VA 23606
Direct: (757) 383-6217
timothy.eas...@urs.com

This e-mail and any attachments contain URS Corporation confidential 
information that may be proprietary or privileged. If you receive this message 
in error or are not the intended recipient, you should not retain, distribute, 
disclose or use any of this information and you should destroy the e-mail and 
any attachments or copies.

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to