That would still be automatically supervised (just not monitored).  The 
building code triggers monitoring systems (previously referred to as 
electrically monitored) keeping in mind that once upon a time many large system 
were not monitored (aka only chains on the valves, just a local bell,  etc).  
When not monitored, it is meant to impact the frequency the system had to be 
inspected.  It is pretty clean in NFPA 25 for Dry pipe where monitoring the low 
temp changed the inspection from daily to weekly and where air pressure is 
monitored inspection went from weekly to monthly.  Pre-Action is not so clean 
were the temp monitoring also changes from daily to weekly but the gauges sit a 
weekly regardless (without really intending to be different IMHO).

We all know tight rigor is applied by the owners doing all these inspections.  
As a side note, the issue of inspection frequencies for gauges has a good 
chance of finally being updated.  Look at the 25 First Draft report when it’s 
published.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Dec 17, 2014, at 4:18 AM, Charles Thurston <[email protected]> wrote:
> 
> Hello Colin,
> 
> I'm no expert, But reading 7.3.2.4.1 the word "automatically" triggered in my 
> mind that if there is less than 20 heads, You still need the compressor. Just 
> don't need the pressure switch to turn the compressor on/off, Maint guy could 
> go by and cycle it daily or as needed. Would still need the low air switch 
> but it is allowed to just ring a bell on the wall.