If the project is required to be designed to NFPA 13, compartmentalizing the combustible attic is not one of the methods listed in NFPA 13 to allow for omission of sprinklers in a concealed combustible space.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 12/17/2014 9:46 AM, Will Crisler wrote:
I have a scenario where the architect is trying to eliminate the requirement
for sprinkler protection in a combustible wood framed attic. This is an
13,000sqft I-4 occupancy. The architect is saying they will be
compartmentalizing the attic into less than 3,000sqft fire areas with the
use of draft curtains. My question is, can the architect do this and still
be code compliant without attic fire protection?

Thanks.

Will Crisler

Southeastern Automatic Sprinkler Co., Inc.

143 Enterprise Dr

P.O. Box 1338

Madison, MS 39110

Ph (601) 898-9385

Fx (601) 898-8230

(800) 898-0238

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to