Thanks Steve

Jeff
JB Fire Protection
Sent from my iPhone

> On Dec 22, 2014, at 18:35, Steve Leyton <[email protected]> wrote:
> 
> Fast Response is a parent category that includes WA and Residential 
> sprinklers.
> 
> Steve L. 
> 
> 
> 
> 
> 
> <div>-------- Original message --------</div><div>From: 
> "[email protected]" <[email protected]> 
> </div><div>Date:12/22/2014  5:48 PM  (GMT-08:00) </div><div>To: 
> [email protected] </div><div>Subject: Re: Do normal 
> yearly fire sprinkler inspections review for    olderheads? </div><div>
> </div>So a QR head is fast response? I was under the impression they were 
> different RTI's
> 
> Jeff
> JB Fire Protection
> Sent from my iPhone
> 
>> On Dec 22, 2014, at 16:46, Duane Johnson <[email protected]> wrote:
>> 
>> QR has an FR element. But FR can also equal RES. FR can also equal extended 
>> coverage standard response or even ESFR. In other words there are many 
>> sprinkler types that have fast response elements. 
>> 
>> Duane Johnson 
>> Strickland Fire Protection
>> Sent from my iPhone
>> 
>>> On Dec 22, 2014, at 6:18 PM, Jeff Bridges <[email protected]> wrote:
>>> 
>>> One additional question also-
>>> IS it QR or FR heads that need to be tested at 20 years/ every 10 
>>> thereafter?
>>> Section 5.1.1.1.3 says fast response elements.
>>> Maybe I'm missing something?
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum 
>>> [mailto:[email protected]] On Behalf Of Roland 
>>> Huggins
>>> Sent: Monday, December 22, 2014 7:55 AM
>>> To: [email protected]
>>> Subject: Re: Do normal yearly fire sprinkler inspections review for older 
>>> heads?
>>> 
>>> It’s NOT part of the annual or the 5 yr.  IT is part of the 20 yr for QR 
>>> and 50 yr for SR.  Technically there is no such thing as an annual 
>>> inspection per NFPA 25.  There are items with an annual frequency but it’s 
>>> not uncommon to check all items with a frequency up to 1 yr during that 
>>> inspection.   Having said that, we had it as part of our old 5 year form 
>>> just to ensure it was recorded somewhere.  It gets an N/A util the system 
>>> is older.
>>> 
>>> Roland
>>> 
>>> 
>>> Roland Huggins, PE - VP Engineering
>>> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
>>> Dallas, TX
>>> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>>> 
>>> 
>>> 
>>> 
>>> 
>>>> On Dec 20, 2014, at 4:02 PM, Jody Massey <[email protected]> 
>>>> wrote:
>>>> 
>>>> I know that this is probably a stupid question...
>>>> 
>>>> I know that NFPA requires the following, but is it part of the annual 
>>>> or 5 year inspection? In other words, do I need to review this myself 
>>>> separately.
>>>> 
>>>> Per NFPA-25, 2011, section 5.3.1.1.1 if sprinklers are 50 years old 
>>>> they shall be replaced or have a representative sample tested. They 
>>>> must be tested every 10 years after that.
>>>> 5.3.1.1.2 states if the sprinklers were manufactured prior to 1920 
>>>> they shall be replaced.
>>>> 5.3.1.1.1.3 states if they are quick response heads, after 20 years 
>>>> they must be replaced or have a sample tested.
>>>> 
>>>> I just need to be sure. Thank you or your insight.
>>>> ᐧ
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>> er.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to