I'm finishing up some specs for fire pumps for some hangars.  USGS for Air 
Force has this:

As a minimum, each pump shall be started automatically 10 times and manually 10 
times, in accordance with NFPA 20.  The fire pumps shall be operated for a 
period of a least
15 minutes and shall not be started more than 2 times in 10 hours.

I don't have heart burn about the 10 vs. 6 or even the 15 minutes vs. 5 from 
NFPA 20.  What I don't follow is not starting the pump more than twice in 10 
hours. As I see it that means it's going to take between 4 and 5 days to fully 
check out the pump.  Anyone know if there is any logic around this?  Any if you 
that do military work and run into this how did you accomplish?  There are 
3-350hp, 1,500 gpm @ 185psi if that makes a difference in your thinking.

I know when I do flows and tampers we'll certainly be starting and stopping 
well more than 2 times in 10 hours. Or do you just start it and let it run for 
several hours when doing this portion? There are 9 systems including 2 foam 
systems so it's not a quick task to run all the water necessary quickly.

If there is a reason for all this down time I'll leave it otherwise I'd think 
the contractor would appreciate getting the testing done in a timely manner.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]<mailto:[email protected]>
www.burnsmcd.com<http://www.burnsmcd.com/>
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For