No. But I did a hybrid chem (plenum and duct) / Hi Ex (surface) over a donut fryer in a Hostess plant (180 sqft of surface).
On Wed, Jan 28, 2015 at 1:51 PM, <[email protected]> wrote: > Did you mean AR-AFFF? > > Yes to the question. Spray application booth using Heptane for degreasing > with potential for accumulation. > > AFFF for non-miscible hydrocarbons, AR-AFFF for miscible polar solvents. > Then there are some universal foams when you have combinations of bad stuff > under the same roof. > > Got a big foam-deluge system pushing about 7500 gpm flow rate on the table > right now. > > We love foam! > > Craig L. Prahl > Fire Protection Group Lead > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29303 > Direct - 864.599.4102 > Fax - 864.599.8439 > CH2MHILL Extension 74102 > [email protected] > > > -----Original Message----- > From: Sprinklerforum [mailto: > [email protected]] On Behalf Of Vince Sabolik > Sent: Wednesday, January 28, 2015 4:42 PM > To: [email protected] > Subject: AFFF??? > > Hey Forum! > > A question for all of you, but most likely for some of the "older" guys.... > > Has anyone here ever sprinklered a spray booth using AFFF or AFFFR? > > I don't think many have. But just so jI know that everyone wasn't out > goofing off and didn't read this, I'd like it you could say "no" in a > response > - either here > or to my email, [email protected] > > ON THE OTHER HAND ... > > if you have done one of these, please let me know what drove the > requirement. > > > thanks, Vince > West Tech Fire Protection, Inc. > > 11351 Pearl Road > > Suite 102 > Strongsville, Ohio 44136 > > > T 440 238-4800 F 440 238-4876C 440 724-7601 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org