NFPA 415 '08 is the latest I have handy.

 4.5.1.3 Passenger-handling areas shall be classified as Ordinary Hazard Group 
1 Occupancy, as defined in NFPA 13, Standard for the Installation of Sprinkler 
Systems, for the purpose of sprinkler system design.

4.5.1.4 Baggage, package, and mail-handling areas shall be classified as 
Ordinary Hazard Group 2 Occupancy, as defined in NFPA 13, Standard for the 
Installation of Sprinkler Systems, for the purpose of sprinkler system design.

Of course the mercantile portions are not passenger handling so that's OHII.

Now is 415 a required document?  Do you really have to follow it? Good 
question.  At best the AHJ could get to it using the matters not provided for 
in IFC.  NFPA 13 does not directly mention concourses thus it's not a matter 
covered would be the argument. 

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gregory Lindholm
Sent: Thursday, January 29, 2015 3:19 PM
To: SprinklerFORUM
Subject: Airport Concourse

What would you design an airport concourse for? I would assume light hazard, 
but I cannot find anything on it.
I could maybe think something else at the baggage carousels, but not the 
seating areas where people are waiting for their planes.

Greg Lindholm                                     
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to