Charles, 

I know ridding is not required; neither is the dielectric union. The Engineer 
already has the cut sheet. We are dealing with someone who is  a little dense. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


> On Feb 4, 2015, at 8:58 PM, Charles Thurston <[email protected]> wrote:
> 
> Hello Todd,
> 
> rodding is not required, Nothing to rod to at the bend on it. Need to send 
> the engineer the cut sheet showing that. I have had to before.
> 
> Wednesday, February 4, 2015, 7:37:16 PM, you wrote:
> 
>> Interesting that I had a client call about this right before this
>> thread started. They installed a 6" unit with the grooved outlet.
>> Now the Engineer on the job is requiring the stub above the floor to
>> be rodded and a dielectric union to be installed.
> 
>> Sent from my iPad
> 
>>> On Feb 4, 2015, at 7:15 PM, Charles Thurston <[email protected]> wrote:
> 
>>> Hello ,
> 
>>>  I use em all the time. GREAT as you can drop it in the ground or give it 
>>> to the site contractor. NO need to hydrotest before they pour the slab.
> 
>>> Wednesday, February 4, 2015, 11:08:19 AM, you wrote:
> 
>>>> It’s a great way to circumvent the need for pit at the lead-in when
>>>> the owner is trying to avoid joints below the slab. This can take
>>>> that joint outside the footprint of the building.
> 
>>>> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire
>>>> Protection Engineer | Fargo, ND | direct: 701.552.9905 | mobile:
>>>> 701.371.5759 | http://www.kfiengineers.com
> 
>>>> -----Original Message-----
>>>> From: Sprinklerforum
>>>> [mailto:[email protected]] On Behalf Of 
>>>> [email protected]
>>>> Sent: Wednesday, February 04, 2015 9:22 AM
>>>> To: [email protected]
>>>> Subject: RE: prefabricated fire riser stub-up
> 
>>>> Yeah that's what I'm talking about.
> 
>>>> Craig L. Prahl
>>>> Fire Protection Group Lead
>>>> CH2MHILL
>>>> Lockwood Greene
>>>> 1500 International Drive
>>>> Spartanburg, SC  29303
>>>> Direct - 864.599.4102
>>>> Fax - 864.599.8439
>>>> CH2MHILL Extension  74102
>>>> [email protected]
> 
> 
>>>> -----Original Message-----
>>>> From: Sprinklerforum
>>>> [mailto:[email protected]] On Behalf Of 
>>>> Travis Mack
>>>> Sent: Wednesday, February 04, 2015 10:20 AM
>>>> To: [email protected]
>>>> Subject: Re: prefabricated fire riser stub-up
> 
>>>> Are you talking about an Ames In-Building Riser?
>>>> http://www.amesfirewater.com/Products/In_Building_Risers
> 
>>>> Travis Mack, SET
>>>> MFP Design, LLC
>>>> 2508 E Lodgepole Drive
>>>> Gilbert, AZ 85298
>>>> 480-505-9271
>>>> fax: 866-430-6107
>>>> email:[email protected]
> 
>>>> http://www.mfpdesign.com
>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
> 
>>>>> On 2/4/2015 8:18 AM, [email protected] wrote:
>>>>> I've got someone asking about a prefabricated, welded stub-up.  Basically 
>>>>> connects to the UG and is one piece up to the connection just above the 
>>>>> slab.
> 
>>>>> I've been hunting but just can't find who makes or represents these.
> 
>>>>> Anyone use these or have a website of manufacturer?
> 
>>>>> Craig L. Prahl
>>>>> Fire Protection Group Lead
>>>>> CH2MHILL
>>>>> Lockwood Greene
>>>>> 1500 International Drive
>>>>> Spartanburg, SC  29303
>>>>> Direct - 864.599.4102
>>>>> Fax - 864.599.8439
>>>>> CH2MHILL Extension  74102
>>>>> [email protected]
> 
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
>>>> ______________________________________________________________________
>>>> This email has been scanned by the Symantec Email Security.cloud service.
>>>> For more information please visit http://www.symanteccloud.com
>>>> ______________________________________________________________________
> 
>>>> ______________________________________________________________________
>>>> This email has been scanned by the Symantec Email Security.cloud service.
>>>> For more information please visit http://www.symanteccloud.com
>>>> ______________________________________________________________________
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> 
>>> -- 
>>> Best regards,
>>> Charles                            mailto:[email protected]
> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> 
> -- 
> Best regards,
> Charles                            mailto:[email protected]
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org