>From the ROC: 
>http://www.nfpa.org/Assets/files/AboutTheCodes/13/13-A2012-ROC.pdf 

13-69 Log #298 AUT-SSI Final Action: Reject
(6.2.1.1)
______________________________________________________________
Submitter: Thomas G. Wellen, American Fire Sprinkler Association, Inc.
Comment on Proposal No: 13-69
Recommendation: Revise text to read as follows:
  6.2.1.1* An existing sprinkler removed for internal pipe inspection as
required by NFPA 25 shall be allowed to be reinstalled in the same outlet as
long as the sprinkler has not been damaged by the removal or reinstallation
process.
  6.2.1.2* An existing sprinkler removed from a pipe drop to drain or relocate
the pipe drop, shall be allowed to be reinstalled in the same pipe drop as long
as the sprinkler has not been damaged by the removal or reinstallation process.
Substantiation: The change for 6.2.1.1 will allow the sprinkler to be re-used
for other procedures as required by NFPA 25 such as a flushing procedure.
   The change for 6.2.1.2 would also allow sprigs, armovers, and branch lines to
be relocated.
Committee Meeting Action: Reject
Committee Statement: The TC doesn't feel that sprinklers should be reused
due to potential damage to operating element or water seal.
Number Eligible to Vote: 29
Ballot Results: Affirmative: 29



Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Duane Johnson
Sent: Friday, February 6, 2015 3:44 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

6.2.1.1 (2013) When a sprinkler has been removed for any reason, it shall not 
be reinstalled.


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Carr
Sent: Friday, February 6, 2015 3:38 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

If he is not pulling the head how is it a violation of NFPA?

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]
904-781-8227


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Duane Johnson
Sent: Friday, February 06, 2015 3:29 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

The problem is, you won't find this in the standard unless you print out the 
ROC...


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Duane Johnson
Sent: Friday, February 6, 2015 3:28 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

Not permitted. There was a proposal submitted on the last cycle to allow this, 
but it was rejected.


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Art Tiroly
Sent: Friday, February 6, 2015 3:29 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

I am having an argument with a contractor that is removing heads and drops then 
moving them to a new position. Sprinklers are QR less than 5 years old.
He is not removing the head from the drop or the 1x1/2 RC. He says he is not 
reusing sprinklers just relocating them with the drop nipple. He says this is 
standard practice. 
Does this violate 6.2.1.1? Do not reuse sprinklers removed from the system.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to