You are correct. Not an issue. 

John

Sent from my iPhone

> On Feb 17, 2015, at 3:20 PM, "Brad Casterline" <[email protected]> 
> wrote:
> 
> I have been fighting the old 'pump room not big enough' frustration and it
> occurred to me the alignment requirements would not apply to an In-Line
> Vertical, right?
> 
> First and foremost is the wording itself; "...parallel to a horizontal
> split-case pump shaft..." , because DUH the shaft on an In-Line Vertical is
> vertical. And with the impeller being horizontal there is not much one can
> do to get equal velocity on each side of the impeller because there is a top
> and bottom instead of sides.
> 
> If this thinking is correct I hope it saves a Sprink some time and
> aggravation down the road.
> 
> 
> 
> thanks,    
> 
> 
> 
> Brad Casterline, NICET IV
> 
> Fire Protection Division
> 
> 
> 
> FSC, Inc.
> 
> P: 913-722-3473
> 
> [email protected]
> 
> www.fsc-inc.com
> 
> 
> 
> Engineering Solutions for the Built Environment
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to