Hi Tom
Thanks for your answer.
I was familiar with these aspects and this confirm it.
I wanted to make sure that an existing standpipe system dated of 1976 in a
condo building of 21 floors was able to withstand the new fire pump
requirements at churn. The standpipe seems to be made entirely of welded joints
(with a min. of schedule 10 piping I assume). In this case, I guess, only the
hose connections will have to be replaced by pressure reducing valves.
Alex
> From: [email protected]
> To: [email protected]
> Subject: RE: Hi-pressure welded schedule 10 joints & fittings
> Date: Sat, 28 Feb 2015 13:59:18 -0500
>
> Alex,
>
> Refer to NFPA 13, 2010, 6.3.2. for Schedule 10 and 40.
>
> You can also check with the major sprinkler system component Suppliers and
> their vendors for Specs on the material.
>
> Regards,
> G. Tim Stone
>
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
>
> 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343
> [email protected]
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Alexandre Lupien
> Sent: Saturday, February 28, 2015 1:51 PM
> To: [email protected]
> Subject: Hi-pressure welded schedule 10 joints & fittings
>
> Hi,
>
> I would like to know if schedule 10 piping with welded joints and fittings
> are approved to withstand hi-pressure (300 lbs) for a standpipe system. If
> not, what about schedule 40.
> Can you refer to the standard mentioning this.
>
> Thanks
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org