Unless somebody messes with the limit switch, the jockey
pump will be "off " on its own, no?



On 3/10/2015 1:29 PM, John Denhardt wrote:
Tim - Please provide a reference for that information.
FYI - NFPA 20 Annex states Jockey Pump "off" setting as minimum static plus 
churn pressure of the fire pump.

John

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tim Stone
Sent: Tuesday, March 10, 2015 12:36 PM
To: [email protected]
Subject: RE: Pump you up?

Don't forget to add about 10 PSI for the Jockey Pump.
City Static + Pump Churn + Jockey Pump 10 PSI =



Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                 117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                            [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Denhardt
Sent: Tuesday, March 10, 2015 12:08 PM
To: <[email protected]>
Subject: Re: Pump you up?

Maximum static plus churn would be my off the cuff answer.

John

Sprinklers Save

On Mar 10, 2015, at 11:55 AM, "Vince Sabolik" <[email protected]> wrote:

Would a fire pump's churn pressure (city static + pump churn)
constitute the operating pressure of a sprinkler system?

The red book has me confused.

Again.


                                            thanks, Vince


West Tech Fire Protection, Inc.
11351 Pearl Road   / Strongsville, Ohio   44136
Phone 440 238-4800    Fax 440 238-4876   Cell  440 724-7601
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




--

West Tech Fire Protection, Inc.
11351 Pearl Road   / Strongsville, Ohio   44136
Phone 440 238-4800    Fax 440 238-4876   Cell  440 724-7601
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to