Chris - how do you check for visible leaks if you can not see the concealed 
piping?

Sprinklers Save

> On Mar 11, 2015, at 5:49 PM, "Cahill, Christopher" <[email protected]> 
> wrote:
> 
> I agree with IOR. But only one needs to be done when the work is complete. 
> The confusion may be a false belief the test needs to be done with exposed 
> pipe. There is no such requirement.
> 
> Chris Cahill
> Fire Protection Engineer
> Burns & McDonnell
> [email protected]
> 952-656-3652 Gary Stites wrote:
> We have run across an interesting situation at a California Hospital. The
> IOR is suggesting that we will be required to hydro the systems twice, once
> at rough-in for a “performance test” and again near final as an “acceptance
> test”. His logic is that all appurtenances are not installed and in place
> at the time of rough-in which is required by the code, thus removing plugs
> and installing sprinklers in flex drops he considers a significant
> modification or “more than a minor” modification, so test twice.
> 
> 
> Anybody have any interpretations or documents that would refute this?
> 
> 
> Gary Stites
> *805-769-GMAN*
> RLH <http://www.rlhfp.com>
> Google+ <https://plus.google.com/101832074405776300082/posts?hl=en>
> Mr. Ricky <http://www.mrricky.net>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to