Viking makes Stainless steel sprinklers.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Morey, Mike
Sent: Thursday, April 02, 2015 1:39 PM
To: [email protected]
Subject: Re: Stainless Steel pipe in sprinkler systems

Typically the cleaning solvents used are not brass/copper friendly.  I'm 
guessing since the request was for stainless pipe the sprinklers will be 
exposed so they'll be some form of corrosion resistant heads (wax/lead?), I 
would assume the heads would be soft enough to seal well but I'll have to pass 
that question on.  

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
[email protected] | www.bmwc.com

________________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Art Tiroly <[email protected]>
Sent: Thursday, April 02, 2015 11:53 AM
To: [email protected]
Subject: RE: Stainless Steel pipe in sprinkler systems

The problem may be joining pipe and outlets. What about copper?


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Morey, Mike
Sent: Thursday, April 02, 2015 9:59 AM
To: [email protected]
Subject: Stainless Steel pipe in sprinkler systems

I'm sure this has been addressed but I'm not finding it after some
searching, are there stainless pipes that fall into the general approvals of
NFPA 13 (I don't have full access to ASTM/ANSI but the stuff called out in
NFPA 13 doesn't seem to be for stainless pipe), or is there specifically
approved stainless pipe/fittings for sprinkler work?  Or will we need to get
a variance based on it being "better"?  We're working in a clean environment
and are probably going to provide socket weld fittings or threaded fittings
and back weld them (other than the heads obviously).  Socket weld fittings
are mentioned, but the only mention of stainless anywhere in the standard is
the C factor table.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
[email protected]<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDt
QSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=mailto%3amanta%40b
mwc.com> |
www.bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQS
kfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=http%3a%2f%2fwww.bmw
c.com%2f>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to