and for Group A plastics >25 ft it is not stated. IT has been flagged as one of the OOPS in the standard to be fixed next cycle (that being 2019 since the 2016 cycle is almost completed).
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Apr 2, 2015, at 3:06 PM, James Crawford <[email protected]> wrote: > > For storage upto 25' use table 16.2.1.4.2.1 and for storage over 25' use > table 16.3.1.1 > > > > Thank you > > > James Crawford > Phaser Fire Protection Ltd. > Phone 604-888-0318 > Fax 604-888-4732 > Cel 604-790-0938 > Email [email protected] > > > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Jamie Seidl > Sent: Thursday, April 02, 2015 2:04 PM > To: [email protected] > Subject: flue space sprinkler spacing > > For the life of me I cannot find the maximum horizontal spacing for in rack > flue sprinklers. > The project is under NFPA 13 2013, Commodity Class III single & double row > racks no solid shelves storage to 30', building height to 36' and I am using > table 16.3.4.1.1.1(c). I know the diagram states that the storage cube is 4 > to 5 feet, and shows sprinklers at every other cube, which would be 10' on > center, but I thought there was something in black and white, or actual > words about that. I'd prefer not to infer. > Any help would be appreciated. > Thanks again for your help, > Jamie Seidl > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org