Good morning, All:
 
I probably missed something, but it seems to me that there  should not be 
any AHJ resistance to so-called "newer/better/improved"  technology offered 
by newer/latest standards - specifically, our beloved  "13"...It seems to me 
that, arguably, rather than attempting to design a  minimal level of 
protection, we are trying to go 'above and beyond' the  older sprinkler 
standards. 
Certainly, QR sprinklers increased levels of  protection in LH occupancies. 
We are on the design/engineering side of this  equation, and it has always 
been my position that when a "PE" signs and seals,  you are probably wise (in 
this instance) to go along with his/her engineering  judgement. So long as 
we do not attempt to design less than the minimum  permitted, I believe we 
are on solid ground. I am still waiting for an AHJ to  actually take on a 
PE/FPE over something like this. Here in New Mexico - based  on nearly 25 
years' residing here - I will put my money on the FPE prevailing,  in a legal 
setting, over the AHJ - that is, if the FPE can adequately defend  his/her 
position.
 
We design sprinkler systems under the 2010 edition of NFPA-13  and one of 
our local AHJ's currently remains under the 1997 UBC/UFC. They might  look 
twice at one of my smaller pipe schedule layouts, however,  they do not blink 
at reviewing our 2010 criteria for sprinklers or fire alarms.  Then again, 
our designs bear the seal of licensed PE/FPE's.
 
It is difficult for me to believe that trying to design  more than the 
minimum (2010 vs., say, NFPA-13/1996) can ever come back  to haunt us. When the 
seal of the PE/FPE appears on sprinkler plans/calc's, the  AHJ should at 
least cooperate unless they believe they have  justifiable grounds to challenge 
the design. Just my 5  cents...
 
Happy Easter to Everyone!!
 
Jerry
[email protected]_ (mailto:[email protected]) 
 
Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.*
Santa Fe, New Mexico USA
(800) 503.1961 nationwide
 
*Licensed Fire Protection Engineers -  Architects/Inspectors/Fire 
Investigators: AZ  CA  CO  NM   NV  NY  TX  UT  KS  MD  MS
 
 
 
In a message dated 4/3/2015 9:00:27 A.M. Mountain Daylight Time,  
[email protected] writes:

My favorite  example of this conundrum goes back to the transition to the 
requirement in 13  for the use of QR sprinklers in Light Hazard, and the 
reduction in design area  allowed by their use.  I believe this occurred in the 
'96 edition -  whatever, our local codes were following earlier editions of 
13.  So when  the engineer specifies to design to the latest edition of NFPA 
13 and follow  state and local codes, what do you do? QR sprinklers at the 
time were more  expensive; but you could get the reduced design area, which 
could save money.  Meanwhile, since the most recent edition of 13 called for 
their use, it was  implied that QR was superior protection to standard 
response in Light Hazard  occupancies.

Galen's response make the most sense, but in my example,  we were a 
contractor competing for a job as a sub-contractor to mechanical -  or maybe 
sub- 
to a sub- of the general. No one cared about such an issue  during bidding. 
If you won the job, no one was going to listen to your  esoteric discussion 
about the benefits of QR sprinklers unless you were  willing to give a deduct 
change order. It was more difficult after receiving  my PE, when I became 
professionally obligated (not just morally) to provide  the best system for 
our customer.

The QR issue was relatively minor and  I am certain no one suffered injury 
because our local codes didn't adopt the  latest version of 13 at that time. 
 But it highlights the challenge and  emphasizes a common point on this 
forum: engineers of record need to be more  engaged in and take more 
responsibility for the fire suppression aspect of  their job. And if the 
opportunity 
is available to contractors (with or without  PEs on staff), they should take 
Galen's advice and propose alternative designs  based on the latest 
standards.

Mark A. Sornsin, P.E. |  Karges-Faulconbridge, Inc. | Fire Protection 
Engineer | Fargo, ND | direct:  701.552.9905 | mobile: 701.371.5759 |  
http://www.kfiengineers.com

-----Original Message-----
From:  Sprinklerforum 
[mailto:[email protected]] On  Behalf Of 
[email protected]
Sent: Thursday, April 02, 2015 7:11  PM
To: [email protected]
Subject: ignoring new  standard requirements

I'm sorry for my grammar and autocorrect as this  is coming from my phone.

How does the forum feel about ignoring the  more stringent requirements of 
the most current NFPA standards all because the  AHJ hasn't adopted the 
latest year?  As the standards have evolved with  each new addition, they 
typically try to clarify murky wording of past  standards, expand on topics, or 
add/change requirements based on the latest  and greatest tests.  So should we 
be purposely designing and installing  and inferior product that more times 
than not is less safe just because the  AHJ hasn't adopted the latest 
design guidelines.  I've heard sometimes  the AHJ doesn't adopt the new 
standard 
simply due to the financial impact of  republishing their amendments and not 
merely because they don't agree.   To me it seems morally/ethically wrong 
but I may just be on my high horse  today.

Thoughts?



Sent from my  iPhone
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This  email has been scanned by the Symantec Email Security.cloud service.
For  more information please visit http://www.symanteccloud.com  
______________________________________________________________________

______________________________________________________________________
This  email has been scanned by the Symantec Email Security.cloud service.
For  more information please visit  http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to