Ohhhh-- this is what threw me:

"The existing hydraulic pipe schedule already in place is going to be used 
to extend the system into the addition."

Brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Tim Stone
Sent: Thursday, April 09, 2015 8:36 AM
To: [email protected]
Subject: RE: Hydraulic Calcs on an existing sprinklered building

Brad, I looked at that too, but in this case it is a hydraulically
calculated system already.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Thursday, April 09, 2015 9:26 AM
To: [email protected]
Subject: RE: Hydraulic Calcs on an existing sprinklered building

I don't think you are missing anything in that you would not have to
calculate it but I find that in 11.2.2. 
You would have to do some flow testing though to make sure of 500 GPM at the
BOR and 15 PSI at the highest, which would be the existing 4th floor.
QR vs SR is another question!

Brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Vince Sabolik
Sent: Thursday, April 09, 2015 8:04 AM
To: [email protected]
Subject: Re: Hydraulic Calcs on an existing sprinklered building

Tim --

If it's a new remote area, definitely. I would probably provide calcs
regardless.

                                                      - Vince


On 4/9/2015 8:56 AM, Tim Stone wrote:
> Hi,
>
>   
>
> I am working on an existing light hazard building that is being 
> remodeled and updated. The four story building (8400SF / floor) was 
> built in 1992
and
> is equipped with a hydraulically calculated sprinkler system. The bulk 
> of the sprinkler system work on this project is to relocate sprinkler 
> heads
to
> new ceiling layout and relocate a few mains and branchlines to 
> accommodate new HVAC.
>
>   
>
> A 1700 SF. 2 story addition is being built on one side and the 
> sprinkler system is to be extended to cover this new space. The 
> existing hydraulic pipe schedule already in place is going to be used 
> to extend the system
into
> the addition.
>
>   
>
> Is it required to perform Hydraulics on this 1700SF addition? 2010 ed. 
> of NFPA 13, 22.4 does not indicate that it is.
>
>   
>
> Am I missing something?
>
>   
>
> Thank you in advance.
>
>   
>
> Regards,
>
> G. Tim Stone
>
>   
>
> G. Tim Stone Consulting, LLC
>
> NICET Level III Engineering Technician
>
> Fire Protection Sprinkler Design
>
> and Consulting Services
>
>   
>
>                  117 Old Stage Rd. - Essex Jct., VT. 05452
>
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>
>                              <mailto:[email protected]> 
> [email protected]
>
>   
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>


-- 

West Tech Fire Protection, Inc.
11351 Pearl Road   / Strongsville, Ohio   44136
Phone 440 238-4800    Fax 440 238-4876   Cell  440 724-7601
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to