No. It is occupied.
There are all 1 story units on Level 1-3. Level 4 has 1½ story units.
1000 sq ft on 4th floor, then go up a set of stairs that is internal to
the unit. The mezzanine/loft is about 400 sq ft. It will have a
bedroom and living space up there as well as a bathroom.
The architect has put confusing notes on the plan. No one can figure it
out. They are conflicting about NFPA 13 then 13R then standpipes, then
no standpipes. He has been asked to clarify, but it is taking longer
than the builder wants. They are just trying to get some ideas to know
how it may go.
If this is a story that would drive standpipes, would it also not drive
the building to an NFPA 13 system since it would then be 5 stories. If
the mezzanine/loft does not count as a story, then it would be
applicable for 13R. They are under 2010 edition. But, if the mezz/loft
does not count as a story to drive it to 13, then does it count as an
elevation to trigger standpipes? Lot's of questions. Not many answers yet.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
On 4/22/2015 9:17 AM, Matthew J Willis wrote:
Sounds like an attic, not a loft.
It will not be occupied right?
R/
Matt
Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
1805 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Cell-605.391.2733
Fax:-605.348.0108
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of David Autry
Sent: Wednesday, April 22, 2015 10:09 AM
To: [email protected]
Subject: RE: Standpipes
Travis,
I can't quote code. We had the same thing and the City required Standpipes.
David Autry
Meininger Fire Protection
2521 West L Street, Suite 5
Lincoln, NE 68522
402.466.2616
402.466.2617 fax
[email protected]
-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Travis Mack
Sent: Wednesday, April 22, 2015 10:38 AM
To: <[email protected]>
Subject: Standpipes
Does a loft/mezzanine count toward the height to require a standpipe?
Example: 4th floor is 29'-4" above lowest level of fire department access.
So standpipe would not be required.
But these units have a loft/mezzanine that will be obviously above the 30'. The
only way to access the loft is from a stair in the unit on the fourth floor.
So standpipes yes or no? It is an R-2 occupancy.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign
Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org