Not all 6 sprinklers but you have to determine the flow based on the SxL rule 
for the 3 sprinklers in that room.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Apr 30, 2015, at 9:21 AM, Jamie Seidl <[email protected]> wrote:
> 
> Roland,
> So if I am reading your response correctly, to use the provisions of
> 8.6.2.1.2, I need to over look the 4 sprinkler design approach and
> calculate the entire room?  It's a little confusing because  11.3.1.2 says
> that "Unless the requirements of 11.3.1.3 are met, the minimum required
> discharge from EACH OF THE FOUR most demanding sprinklers shall be greater
> of the following: (1) In accordance with minimum flow rates indicated in
> individual listings. (2) Calculated based on delivering a minimum of 0.1
> gpm/sqft over the desing area in accordance with the provisions of 8.5.2.1
> or 8.6.2.1.2."  A quick scratch paper write up we would be delivering .21
> gpm/sqft 6x21= 126 gpm/600sqft) because we still default to the minimum
> flows, (in this case 21 gpm/sprinkler)
> 
> On Thu, Apr 30, 2015 at 11:41 AM, Roland Huggins <[email protected] 
> <mailto:[email protected]>
>> wrote:
> 
>> very interesting question. To restate the question (since you have
>> received answers on different nuances), we are looking at whether or not
>> you can apply the small room rule to part of the sprinklers in the room
>> (the room is 600 sf and has 6 sprinklers, you calculate the area per
>> sprinkler by 600 / 6 for 100 sf per sprinkler then apply that to only 3 of
>> the sprinklers to total 4 sprinklers with 1 from the adjacent room).  I
>> would say no.  The current wording leaves that unanswered  since it only
>> tells you how to determine the area (as shown below).  Keep in mind that
>> the rule grew out of the 1500 sf minimum days so all sprinklers had to be
>> included.  This connection to the whole room is better indicated by the new
>> text for the 2016 ed also shown below.  You have to deliver 0.1 over the
>> room aka the whole room. The issue you asked was not the basis for the
>> change.  Some were interpreting that the small room rule applied only to
>> pendent sprinkler because it was located in 8.6.  They had a point since as
>> I preach often enough - LOCATION HAS MEANING.  Nonetheless, it was the
>> process that was being identified an not the sprinkler type but this is a
>> much better approach.
>> 11.3.1.3(2) Calculated based on delivering a minimum of 0.1 gpm/ft2 (4.1
>> mm/min) over the design area in accordance with the provisions of 8.5.2.1
>> or 8.6.2.1.2
>> 
>> 8.6.2.1.2 The requirements of 8.6.2.1.1 shall not apply in a small room as
>> defined in 3.3.21.
>> 
>> 8.6.2.1.2.1 The protection area of coverage for each sprinkler in the
>> small room shall be the area of the room divided by the number of
>> sprinklers in the room.
>> 
>> 2016 ed - 11.3.1.3(3)   In rooms or compartments 800 ft2 (74.3 m2) or less
>> calculated based on delivering a minimum of 0.1 gpm/ft2 (4.1 mm/min) over
>> the room or the compartment using the area of the room divided by the
>> number of sprinklers in the room
>> 
>> With this being an interpretation (and not something I can claim  BUT IT’S
>> EXPLICIT), I’m adding the NFPA caveat.  As  a TC member, this is my
>> interpretation and not to be considered a formal interpretation of NFPA or
>> any of its technical committees.
>> 
>> Roland
>> 
>> Roland Huggins, PE - VP Engineering
>> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
>> Dallas, TX
>> http://www.firesprinkler.org <http://www.firesprinkler.org/> 
>> <http://www.firesprinkler.org/ <http://www.firesprinkler.org/>>
>> 
>> 
>> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> <mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to