I hate to tell you but the below changes nothing. I don't see where mechanical rooms without stockpiles are addressed. Mechanical rooms with stockpiles by DESIGN are not all that common. I'm not arguing in PRACTICE they are usually used for storage. FWIW I treat them as OHII but in tight water situations when they are small or only have air handlers then OHI would suffice.
Chris Cahill, PE* Associate Fire Protection Engineer Burns & McDonnell Phone: 952.656.3652 Fax: 952.229.2923 [email protected] www.burnsmcd.com *Registered in: MN Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For > > > -----Original Message----- > From: Sprinklerforum > [mailto:[email protected]] On Behalf Of > Tom Wellen > Sent: Wednesday, May 06, 2015 11:25 AM > To: [email protected] > Subject: Re: Light & OH1 Hazard From Same Riser > > The next edition, 2016 will address mechanical rooms in the annex. > > I submitted PI No. 514 to address mechanical rooms: > > Public Input No. 514-NFPA 13-2013 [ Section No. A.5.3.1 ] > A.5.3.1 > Ordinary hazard (Group 1) occupancies include occupancies having uses and > conditions similar to the following: > (1) Automobile parking and showrooms > (2) Bakeries > (3) Beverage manufacturing > (4) Canneries > (5) Dairy products manufacturing and processing > (6) Electronic plants > (7) Glass and glass products manufacturing > (8) Laundries > (9) Restaurant service areas > (10) Mechanical rooms with stockpiles up to 8 ft > > Statement of Problem and Substantiation for Public Input A new mechanical > room by definition is a light hazard occupancy. The room is empty and the > equipment is generally noncombustible. The AHJ likely will not buy off that > the room will not be used for storage. > > I also submitted Public Input No. 515-NFPA 13-2013 [ Section No. A.5.3.2 ] > that was rejected: > A.5.3.2 > Ordinary hazard (Group 2) occupancies include occupancies having uses and > conditions similar to the following: > ...... > (31) Mechanical rooms with stockpiles up to 12 ft > > Committee Statement > Resolution: The definition of OH2 will drive the user to this occupancy > hazard classification. This language is superfluous. > > > Tom Wellen > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org