A general rule of thumb is you can run CPVC anywhere sprinklers are not required. If you want to run CPVC in an area where sprinklers are required, you have to use sprinklers that are specially listed to allow CPVC in those spaces.

If you had an office building that was framed in steel, then you could use CPVC.

Your case is very similar. You want to run the piping in a non-combustible area and supply pendent sprinklers in the ceilings. I don't believe that violates any listings of the CPVC piping.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 5/20/2015 8:38 AM, Sean Lockyer wrote:
I have an interesting question to ask of everyone here. I am being asked to 
install an NFPA  13, non-residential sprinkler system in a small, new building 
that will be constructed with wood. However, the wood trusses will consist of 
fire rated lumber with a flamespread rating of less than 25, which will not 
require sprinkler protection since they would considered to then be 
non-combustible, or at the worst, limited combustible.

With that being said, could you then install CPVC piping in these concealed 
areas without also having to use the specially listed concealed sprinklers 
(such as the CC1, CC2, HIP, BB1, etc.) heads that Tyco makes ?

Remember, you can only install CPVC in an attic or a combustible concealed 
space if you also use those specially listed heads but if the area is 
technically not combustible I would say that you could use CPVC just like if 
you were using CPVC above an gyp board ceiling in an office for example - if 
you take the listing literally.

What does everyone else think ?


               Sean Lockyer
               Project Designer                               4617 Parkbreeze 
Court
               Cell    386-279-1197                              Orlando, 
Florida 32808
               [email protected]              Phone:      407-816-9101
               www.AITLifeSafety.com                       Fax:         
407-816-9104


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to