That is the precise justification. I'd like to think the fire service would simply use their on board pump and boost the FDC when and if they need that extra 20 or 30 psi, instead of adding that cost to every building. My justification is that for 99% of the responses, 100psi is sufficient and the 1% is costing between $100,000 and $200,000 per building to accommodate.
Mark at Aero 602 820-7894 Sent from my iPhone > On Jun 19, 2015, at 5:03 PM, "Cahill, Christopher" <[email protected]> > wrote: > > Many should. That would be 200' of 1 1/2" hose with a 100 psi nozzle. Very > common setup on the fire service. But I suspect few actually have this > requirement. > > Chris Cahill > Associate Fire Protection Engineer > Burns & McDonnell > 952-656-3652 > [email protected]<mailto:[email protected]> > On Jun 19, 2015 6:45 PM, "[email protected]" <[email protected]> wrote: > Just a follow up to my survey of the local application of requirements for > standpipe design pressure a few weeks ago. > > Does any AHJ require 130 PSI minimum design pressure on a class I Wet > Automatic Standpipe? > If you are an AHJ and require this, please contact me off forum for > discussion. > If anyone knows of a jurisdiction requiring this please post. > Thanks all > Have a great Father's day Weekend > > Mark at Aero > 602 820-7894 > [email protected] > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
