Late last year I took a shot at getting through the sticky wicket of 8.3.3.5
with:

My take is this:
 example 1-- Light Hazard-- Q.R. required-- Sprinkler= "Acme Model A" listed

Q.R. at max 14 x 14 and S.R. up to 20 x 20-- so max spacing = 14 x 14.
 example 2-- Ord Haz-- same sprinkler-- max spacing = 20 x 20, BUT if it 
happens that some coverage areas are 14 X 14, it is NOT considered mixing
Q.R. 
and S.R.

and got this atta boy:

Brad, correct. That was the intent of the committee.

Peter Schwab
VP of Purchasing & Engineering Technologies

I was on cloud nine the rest of the year ;)

Brad


-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of T. Silva
Sent: Tuesday, July 07, 2015 4:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Mixing EC sprinklers with Std coverage sprinklers

That lays it to rest, Thanks, Larry, 
Tony


----- Original Message -----

From: "Larry Keeping" <lkeep...@plcfire.com> 
To: sprinklerforum@lists.firesprinkler.org 
Sent: Tuesday, July 7, 2015 12:57:12 PM 
Subject: RE: Mixing EC sprinklers with Std coverage sprinklers 

Just as a point of information, I thought I should relate to you the new
text that will be entered into the forthcoming 2016 edition of NFPA 13: 

8.3.3.2 Where quick-response sprinklers are installed, all sprinklers within
a compartment shall be quick- response unless otherwise permitted in 8.3.3.3
, 8.3.3.4 , or 8.3.3.5 . 

8.3.3.3 Where there are no listed quick-response sprinklers in the
temperature range required, standard- response sprinklers shall be permitted
to be used. 

8.3.3.4 The provisions of 8.3.3.2 shall not apply to in-rack sprinklers. 

8.3.3.5 Where a sprinkler carries a listing for both standard-response
protection and quick-response protection at different coverage areas, that
sprinkler shall be permitted to be installed within a compartment at the
spacing for both the quick-response and standard-response listings without
any separation between the areas so covered. 

8.3.3.6 When existing light hazard systems are converted to use
quick-response or residential sprinklers, all sprinklers in a compartment
shall be changed. 

I think that this will satisfy your concerns - at least in the future. 

Best regards 

Larry Keeping 

-----Original Message----- 
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Fairchild, Jack 
Sent: July-07-15 1:01 PM 
To: sprinklerforum@lists.firesprinkler.org 
Subject: RE: Mixing EC sprinklers with Std coverage sprinklers 

What Scot said, but the most conservative answer is once an EC head is
installed with the small spacing it is by nature QR and all heads in the
space would need to be QR. 

Jack Fairchild 


-----Original Message----- 
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Greg McGahan 
Sent: Tuesday, July 07, 2015 10:26 AM 
To: sprinklerforum@lists.firesprinkler.org 
Subject: Re: Mixing EC sprinklers with Std coverage sprinklers 

I lost the original question ...but I think that the AFSA has a recent
informal interp related to this issue 


Greg McGahan 
Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 
1160 McKenzie Road 
Cantonment, FL 32533 
850-937-1850 
fax 850-937-1852 

On Tue, Jul 7, 2015 at 9:07 AM, å... .... <eurekaig...@gmail.com> wrote: 

> Interesting question. If the activation temperatures are close to the 
> same value, then I would match the RTI of the standdard sprinklers 
> with the imputed RTI of the EC. 
> 
> An obvious caveat is if the specifications or engineeering report 
> stipulate the QR in this compartment. 
> 
> The NFPA 13 intent, I believe, is to prevent QR sprinklers from 
> activating when they are further away from the fire, in the presence 
> of SR sprinklers when these SR sprinklers are nearer to the fire. 
> 
> If the compartment is smaller than the design area,...then the case 
> can be made that the hydraulic design will account for all sprinklers 
> activating, regardless of their intended order of activation (1st 
> ring, 2nd ring, etc.) as manipulated by the RTI of the sprinkler. 
> Consider what is to be protected from fire by the different sprinklers 
> and modify your judgment accordingly. 
> 
> Scot Deal 
> Excelsior Fire/Risk Engineering 
> _______________________________________________ 
> Sprinklerforum mailing list 
> Sprinklerforum@lists.firesprinkler.org 
> 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl 
> er.org 
> 
_______________________________________________ 
Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________ 
Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________ 
Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to