I won't quote the numbers of the case we recently heard about-- the
sprinklers were way up there, under a metal deck, non-conditioned space, hot
day, no pressure relief-- but I was pretty astounded at the increase in
pressure above normal city static.
Brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of James McHugh
Sent: Tuesday, July 14, 2015 2:34 PM
To: [email protected]
Subject: RE: Air Venting in NFPA 13 (2016)

Brad,
 Very good point. 
Jim McHugh

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Tuesday, July 14, 2015 2:26 PM
To: [email protected]
Subject: RE: Air Venting in NFPA 13 (2016)

Thanks Peter.

I just wanted to say that if contractor's start venting practices on
existing systems, through remote Insp. Test. Conn., aux. drains, ect, for
piping in areas subject to high ambient temperature, it would be a good idea
to make sure there is a 1/2" pressure relief valve. The 'air cushion idea'
is not a myth!!

Brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Pete Schwab
Sent: Tuesday, July 14, 2015 12:44 PM
To: [email protected]
Subject: RE: Air Venting in NFPA 13 (2016)

It should be in the 2016 edition unless someone successfully appeals to the
Standards Council and they overturn the floor action (highly unlikely)

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com







-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Tuesday, July 14, 2015 11:04 AM
To: [email protected]
Subject: Air Venting in NFPA 13 (2016)

Am I understanding correctly that air venting will be required 13-2016?

 

There was a motion to NOT require it, but that motion failed, right?

 

thanks,

 

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to