Thanks Jim. I won't quote the numbers of the case we recently heard about-- the sprinklers were way up there, under a metal deck, non-conditioned space, hot day, no pressure relief-- but I was pretty astounded at the increase in pressure above normal city static. Brad
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of James McHugh Sent: Tuesday, July 14, 2015 2:34 PM To: [email protected] Subject: RE: Air Venting in NFPA 13 (2016) Brad, Very good point. Jim McHugh -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brad Casterline Sent: Tuesday, July 14, 2015 2:26 PM To: [email protected] Subject: RE: Air Venting in NFPA 13 (2016) Thanks Peter. I just wanted to say that if contractor's start venting practices on existing systems, through remote Insp. Test. Conn., aux. drains, ect, for piping in areas subject to high ambient temperature, it would be a good idea to make sure there is a 1/2" pressure relief valve. The 'air cushion idea' is not a myth!! Brad -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Pete Schwab Sent: Tuesday, July 14, 2015 12:44 PM To: [email protected] Subject: RE: Air Venting in NFPA 13 (2016) It should be in the 2016 edition unless someone successfully appeals to the Standards Council and they overturn the floor action (highly unlikely) Peter Schwab VP of Purchasing and Engineering technologies Wayne Automatic Fire Sprinklers Inc. 222 Capitol Court Ocoee, Fl 34761 Mobile: (407) 468-8248 Direct: (407) 877-5570 Fax: (407) 656-8026 www.waynefire.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brad Casterline Sent: Tuesday, July 14, 2015 11:04 AM To: [email protected] Subject: Air Venting in NFPA 13 (2016) Am I understanding correctly that air venting will be required 13-2016? There was a motion to NOT require it, but that motion failed, right? thanks, Brad Casterline, NICET IV Fire Protection Division FSC, Inc. P: 913-722-3473 [email protected] www.fsc-inc.com Engineering Solutions for the Built Environment _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org