With regards to options; #1 - deflector 1-6 inches below the member to a maximum of 22" #2 - deflector at or above the bottom of the member to a maximum of 22" (obs rules from 8.6.5.1.2 must be followed) #3 - Installed in each bay to a maximum of 12" #4 - Wood joists (NA) #5 - Concrete tees, deflector 1" below the member with no maximum deflector to ceiling distance.
You're not limited to #5, but you can use it if #1 or #2 will not work due to the depth of the tee. Hope that helps. Eric V. Tysinger Designer Wiginton Fire Systems - Miami, FL Email: [email protected] Main: 305-888-2402 Direct: 305-830-0490 Fax: 305-888-3804 Mobile: 239-633-9703 Confidentiality Notice: This e-mail message, including any attachments, is for the sole use of the intended recipients and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply e-mail and destroy all copies of the original message. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Monday, August 10, 2015 9:24 AM To: [email protected] Subject: Obstructed Construction Clarification Working on an old building that has exposed concrete tee's for the roof deck. Section 8.6.4.1.2 (2007) says that heads must be installed per one of the listed (5) options, however #5 specifically addresses concrete tee's where none of the other four do, am I therefore limited to only option #5? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org