I would check with local water jurisdictions. There are a couple of water companies in our area that only allow 2" lines for residential.
Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.526.7443 cell www. AFPsprink.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Tuesday, August 18, 2015 1:22 PM To: [email protected] Subject: 2" Residential Supply For Coolers Quick question: Is there anything that allows or disallows the use of a 2" domestic underground to supply sprinklers being added to (2) coolers in an existing building? From what I understand there are no other sprinklers in the building other than the ones they want added to the coolers. I assume the water demands for OH-2 plus hose for 60-90 minutes would still need to be met? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org