I have a specific question for the forumites and any 13 TC members willing to 
weigh in on the issue. The question: "Is it acceptable to install an ESFR 
sprinkler head directly below a skylight measuring 4'x8' (32 SF) where the 
general area ceiling to deflector distance is 12" and the top of the skylight 
to deflector distance is 24" up to 30"?" 

My path through NFPA 13 2010 Edition starts at 8.5.1, then 8.5.1.3, then 
8.5.4.1.1,  8.5.7, 8.5.7.1, and finally 8.12.4.1. 

Paraphrasing;

8.5.1 General -  tells us that sprinklers shall be located, spaced, and 
positioned properly. 
8.5.1.3  tells us that the requirements of 8.5.2 through 8.5.7 SHALL APPLY TO  
ALL SPRINKLER TYPES (emphasis mine) unless modified by more restrictive rules 
in 8.6 through 8.12. 
8.5.4.1.1 tells us the deflector distance to ceiling is determined by the 
sprinkler type and construction type.
8.5.7 Skylights, 8.5.7.1 and.2 tell us that we are not required to install 
sprinkler heads in skylights (or ceiling pockets)meeting certain specific 
requirements (which we do). 
8.12.4 ESFR Deflector Below Ceilings - Nothing in the text of this section 
states an exception to 8.5.7.1.  
 
Any comments are appreciated.