Width, per nfpa 13, is the shorter of the two dimensions.

On Thu, Aug 20, 2015 at 10:55 PM, å... .... <[email protected]> wrote:

> Your self-storage building feature a hallway-cloud design with financially
> inconvenient prescriptive sprinkler implications.
>
> What about the "width" as measured n the direction parallel with the
> hallway?  The obstruction length in that direction exceeds 4 feet.   Though
> stored goods in quantity should not be in the hallway for substantial
> amounts of time, and if a fire were to occur in
> hallway-located-combustibles, the fire likely would not advance into the
> storage rooms (liquid fuels being the exception, but even then there are
> sprinklers in the storage rooms).  If I were writing the specification for
> bid on this project, I would have declared that sprinklers cover the
> 60-inich wide hallway at the lower cloud level before they covered the
> hallway at the obstructed ceiling level.
>
>
> Scot Deal
> Excelsior Fire/Risk Engineering