Seeing how NFPA 13 defines a system riser as an above ground horizontal or
vertical pipe **between the water supply and the cross or feed mains** that
contains a control valve etc... I would say your option 'A' would be the
best fit for a manifold system.  For a single riser it makes sense that BOR
is at the supply flange, 6" A.F.F.



On Fri, Aug 21, 2015 at 7:31 AM, Ed Kramer <[email protected]> wrote:

> This may have been discussed previously, I don't recall.
>
> Assume  an underground fire service enters a building, multiple system
> risers are located in an interior mechanical room approx 50' from the
> stub-in location.  In the mechanical room there is a backflow prevention
> device and multiple system risers.  Where is the "base of riser" - you
> know,
> the "base of riser" that listed on the hydraulic design placard?
>
> a)      At the bottom of each individual system riser - a slightly
> different
> physical location for each system?
>
> b)      At the discharge side of the backflow prevention device?
>
> c)      At the inlet side of the backflow prevention device?
>
> d)      At the underground flange?
>
>
>
> I'm curious how others see this.
>
>
>
> Ed Kramer
>
> Lawrence, KS
>